Having been an electrician for 19 years I can categorically say that the formula is correct.
If I have say 0.30 end to end for my line conductor and 0.50 end to end for my cpc’s (2.5mm T+E) then when I measure at each socket outlet with the cross connection method, then I will measure 0.20 ohms for my R1+R2 measurement.
The calculation/formula is indeed correct.

For same size conductors say 2.5mm then my R1+R2 will be half of my measured r1 ,rn and r2 end to ends, in this example 0.15ohms.
It’s a simple resisters in parallel calculation clearly explained in GN3.

We are splitting hairs here maybe I’ll measure 0.21 at some sockets maybe 0.20 at some and maybe 0.19.

Thank you replying. The way I see it is that there are two formula at play here. The recognised formula for resistors in parallel (1/R=1/R1 + 1/R2) and the derived formula for RFCs (R=(r1+r2)/4). Using your own example of 0.3 r1 and 0.5 r2, the recognised formula gives R as 0.225 ohms and the derived formula gives 0.2 ohms (as you say). This difference is negligible, would be within the 0.05 ohm tolerance and ignored in the real world. However the difference is there. If you take a more exaggerated example, say r1=4 and r2 =12 - the recognised formula gives 3 ohms but the derived formula gives 4 ohms - a significant difference. As "happysteve"says in #23 below " (Q) Does R1+R2 always equal (r1+r2)/4? (A) If half way round the circuit, OR CSAs are equal then yes, otherwise.....well not quite but close enough". That was the point if my original post.
 
Yes, half way round the ring is the worst case - and that's what matters for fault protection etc. Anywhere else on the ring will have a lower value - as demonstrated by the graph posted (whichever way up you look at it) :p
The different lines on the graph are irrelevant. The deviations from the simplistic formula only occur away from the centre point of the ring - where the resistance is lower than the worst case anyway.

But for a simple explanation ...
Consider a fault at the midpoint of the ring. From the MCB in the CU to the fault, you have two equal conductors in parallel - each of which is half the length of the ring and hence has half the resitance of the whole ring. So you have two resistors of value r1/2 in parallel, and two equal resistors in parallel give you half the value of each of them. So you have (r1 / 2) / 2, or r1 / 4.
The CPC has the same calculation, so from MET to fault you have r2 / 4.
So total is (r1 / 4) + (r2 / 4), which is better written as (r1 + r2) / 4
Again, this is the worst case, at any other pointbround thecring, the total resistance to the fault will be lower. So you don't need to considervthe effects of different line & CPC sizes etc. This even hold true if the cable CSA changes round the ring IF you consider "middle of the ring" to be in terms of cable resistance rather than distance.
It would be a diffetent case if the CSA variations were "odd" - eg if in one leg you had a larger line, and in the other leg you had a larger CPC. But that would be unusual !
 

Reply to (r1+r2)/4, the myth expelled? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
764
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring...
Replies
23
Views
26K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
M
This problem solving was on Virtual Scenarios (Ring Final Circuit) Getting Value of R1+R2 2.5mm and 1.5mm size cable used. 1st From the C.U...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock