Discuss (r1+r2)/4, the myth expelled? in the UK Electrical Forum area at ElectriciansForums.net
remainder of what you bin drinking will do.
I do enjoy my Saturdays lol.
r1+r2 is halved cause its half the length (agreement on that), then the formula needs another division of 2 to satisfy (division of 4). So in that case its half the remainder
Yes, which will give us the R1 + R2.
The second halving is required because we have two conductors in parallel which reduces the resistance by half.
I wrote a Matlab script a while ago to determine the deviation from equality between R1+R2, and r1+r2/4, when the cpc and line conductors are different sizes.
For the different sizes of T&E available, the maximum discrepancy at the very edges of the ring was 20% (with 4+1.5mm cable); for 2.5+1.5mm, the maximum discrepancy was about 6%. If you've got old 2.5+1mm, you might get as much as 18%.
For all practical purposes, it's as near as Phuket is to swearing.
was already strarrrtiiing to see doublle .happpy stevesss graph finnishhed time for bed seddd zebeddeee. boiiing. .
How have you measured R1 + R2, to compare to r1 + r2 / 4?
The main bit of the code is like this:
Code:
    for c=1:length(percentage_round_loop); % c keeps track of which array index we're at,
                                           % as we go round the percentage
                                           % loop
        R_ratio = 1 / csa_ratio; % resistance ratio is the inverse of CSA ratio
        % (LS = Line at socket, ES = Earth at socket)
        %     LS        ES
        %   __|__     __|__
        %  _|_ _|_   _|_ _|_
        %  |A| |B|   |C| |D|
        %  |_| |_|   |_| |_|
        %   L1  L2    E1  E2
        %   |   |_____|   |
        %   |_____________|
        %        (CU)
        % ... which is exactly the same as:
        %            _____      _____
        %        ---|__A__|----|__D__|---
        % LS ----|   _____      _____   |---- ES
        %        ---|__B__|----|__C__|---
        A = percentage_round_loop(c);
        B = max_percentage_around_loop - percentage_round_loop(c); % has to add up to 100%
        C = percentage_round_loop(c) * R_ratio; % CPC is smaller, so higher resistance
        D = (max_percentage_around_loop - percentage_round_loop(c)) * R_ratio;
        scaling_factor = ( max_percentage_around_loop * (1 + R_ratio) ) / 4;
        % scaling_factor normalises the graph, so that if R1+R2 ==
        % (r1+r2)/4, the answer would be 1
        A = A / scaling_factor;
        B = B / scaling_factor;
        C = C / scaling_factor;
        D = D / scaling_factor;
        r1 = A + B; % r1 is your P loop resistance
        r2 = C + D; % r2 is your CPC loop resistance
        R1_plus_R2(c) = ((A+D) * (B+C)) / (A+B+C+D);
        % resistors in parallel: product over sum (resistors in series
        % added, ie (A+D) in parallel with (B+C)
    end
Are we all clear? :)
Code:
                                           % loop
        %     LS        ES
        %   __|__     __|__
        %  _|_ _|_   _|_ _|_
        %  |A| |B|   |C| |D|
        %  |_| |_|   |_| |_|
        %   L1  L2    E1  E2
        %   |   |_____|   |
        %   |_____________|
        %        (CU)
        %            _____      _____
    end
:oops:
Reply to (r1+r2)/4, the myth expelled? in the UK Electrical Forum area at ElectriciansForums.net
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring...
27K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
5K
M
This problem solving was on Virtual Scenarios (Ring Final Circuit) Getting Value of R1+R2 2.5mm and 1.5mm size cable used. 1st From the C.U...