r1+r2 is halved cause its half the length (agreement on that), then the formula needs another division of 2 to satisfy (division of 4). So in that case its half the remainder
Yes, which will give us the R1 + R2.
The second halving is required because we have two conductors in parallel which reduces the resistance by half.
 
I wrote a Matlab script a while ago to determine the deviation from equality between R1+R2, and r1+r2/4, when the cpc and line conductors are different sizes.

For the different sizes of T&E available, the maximum discrepancy at the very edges of the ring was 20% (with 4+1.5mm cable); for 2.5+1.5mm, the maximum discrepancy was about 6%. If you've got old 2.5+1mm, you might get as much as 18%.

r1_plus_r2_over_4.png

For all practical purposes, it's as near as Phuket is to swearing.
 
was already strarrrtiiing to see doublle .happpy stevesss graph finnishhed time for bed seddd zebeddeee. boiiing. .
 
I wrote a Matlab script a while ago to determine the deviation from equality between R1+R2, and r1+r2/4, when the cpc and line conductors are different sizes.

For the different sizes of T&E available, the maximum discrepancy at the very edges of the ring was 20% (with 4+1.5mm cable); for 2.5+1.5mm, the maximum discrepancy was about 6%. If you've got old 2.5+1mm, you might get as much as 18%.

View attachment 50886

For all practical purposes, it's as near as Phuket is to swearing.
How have you measured R1 + R2, to compare to r1 + r2 / 4?
 
How have you measured R1 + R2, to compare to r1 + r2 / 4?

The main bit of the code is like this:

Code:
    for c=1:length(percentage_round_loop); % c keeps track of which array index we're at,
                                           % as we go round the percentage
                                           % loop
        R_ratio = 1 / csa_ratio; % resistance ratio is the inverse of CSA ratio
        
        % (LS = Line at socket, ES = Earth at socket)
        %     LS        ES
        %     |         |
        %   __|__     __|__
        %   |   |     |   |
        %  _|_ _|_   _|_ _|_
        %  | | | |   | | | |
        %  | | | |   | | | |
        %  |A| |B|   |C| |D|
        %  | | | |   | | | |
        %  |_| |_|   |_| |_|
        %   |   |     |   |
        %   |   |     |   |
        %   L1  L2    E1  E2
        %   |   |     |   |
        %   |   |_____|   |
        %   |_____________|
        %        (CU)
        %
        % ... which is exactly the same as:
        %            _____      _____
        %        ---|__A__|----|__D__|---
        % LS ----|   _____      _____   |---- ES
        %        ---|__B__|----|__C__|---
        
        
        A = percentage_round_loop(c);
        B = max_percentage_around_loop - percentage_round_loop(c); % has to add up to 100%
        C = percentage_round_loop(c) * R_ratio; % CPC is smaller, so higher resistance
        D = (max_percentage_around_loop - percentage_round_loop(c)) * R_ratio;

        scaling_factor = ( max_percentage_around_loop * (1 + R_ratio) ) / 4;
        % scaling_factor normalises the graph, so that if R1+R2 ==
        % (r1+r2)/4, the answer would be 1

        A = A / scaling_factor;
        B = B / scaling_factor;
        C = C / scaling_factor;
        D = D / scaling_factor;
        r1 = A + B; % r1 is your P loop resistance
        r2 = C + D; % r2 is your CPC loop resistance

        R1_plus_R2(c) = ((A+D) * (B+C)) / (A+B+C+D);
        % resistors in parallel: product over sum (resistors in series
        % added, ie (A+D) in parallel with (B+C)
    end

Are we all clear? :)
 
The main bit of the code is like this:

Code:
    for c=1:length(percentage_round_loop); % c keeps track of which array index we're at,
                                           % as we go round the percentage
                                           % loop
        R_ratio = 1 / csa_ratio; % resistance ratio is the inverse of CSA ratio
       
        % (LS = Line at socket, ES = Earth at socket)
        %     LS        ES
        %     |         |
        %   __|__     __|__
        %   |   |     |   |
        %  _|_ _|_   _|_ _|_
        %  | | | |   | | | |
        %  | | | |   | | | |
        %  |A| |B|   |C| |D|
        %  | | | |   | | | |
        %  |_| |_|   |_| |_|
        %   |   |     |   |
        %   |   |     |   |
        %   L1  L2    E1  E2
        %   |   |     |   |
        %   |   |_____|   |
        %   |_____________|
        %        (CU)
        %
        % ... which is exactly the same as:
        %            _____      _____
        %        ---|__A__|----|__D__|---
        % LS ----|   _____      _____   |---- ES
        %        ---|__B__|----|__C__|---
       
       
        A = percentage_round_loop(c);
        B = max_percentage_around_loop - percentage_round_loop(c); % has to add up to 100%
        C = percentage_round_loop(c) * R_ratio; % CPC is smaller, so higher resistance
        D = (max_percentage_around_loop - percentage_round_loop(c)) * R_ratio;

        scaling_factor = ( max_percentage_around_loop * (1 + R_ratio) ) / 4;
        % scaling_factor normalises the graph, so that if R1+R2 ==
        % (r1+r2)/4, the answer would be 1

        A = A / scaling_factor;
        B = B / scaling_factor;
        C = C / scaling_factor;
        D = D / scaling_factor;
        r1 = A + B; % r1 is your P loop resistance
        r2 = C + D; % r2 is your CPC loop resistance

        R1_plus_R2(c) = ((A+D) * (B+C)) / (A+B+C+D);
        % resistors in parallel: product over sum (resistors in series
        % added, ie (A+D) in parallel with (B+C)
    end

Are we all clear? :)
:oops:
 

Reply to (r1+r2)/4, the myth expelled? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
763
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Replies
4
Views
3K
Hi...keen amateur here......don't crucify me for asking!! I understand Ohm's law and I understand the mechanics of measuring end to end on ring...
Replies
23
Views
26K
Eh up :) I don't do EICRs - not enough experience - but the things I see on some reports done by others really dismay me. Perhaps some of my...
Replies
21
Views
5K
D
M
This problem solving was on Virtual Scenarios (Ring Final Circuit) Getting Value of R1+R2 2.5mm and 1.5mm size cable used. 1st From the C.U...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.