davino
couple of questions...in regards to r1 r2, when testing what is the lowest reading thats accepted on say a 1.5 t&e, to a 10.0 t&e I got a reading of 0.39 on a 10mm t&e and I got a right -------in for puttin it on the sheet..
and is this the right calculation for pfc? voltage divided by Ze? so if my voltage is 230v and the Ze is 0.12 the answer is 1966 which is around 1.9Ka ???
someone please tell me this is right am gettin a right grilling from my boss ...
Hi,
Firstly your calculation for PFC works out at 1.9KA which seems like a reasonable reading in my experience. With regards your r1+r2 - it obviously depends on the length of the cable. The most important things to be considering with regards limits, is the voltage drop at the end of the cable and the measured Zs. Make sure youre nulling your test leads first! :D
In the back of the OSG you will find a table for reisistance of cables per metre so if you know the approx length then you can check against it,
PFC is the highest of Pscc and Pefc.
Pscc (prospective short circuit current) is the short circuit current between 'Live' conductors ie in single phase between Line & Neutral and in three phase between Line conductors.
Pefc (prospective earth fault current) is the the short circuit current between line and earth. So Pefc is Uo/Ze.
For three phase Pscc is taken as 2x line neutral fault current.
Reply to r1 r2 and pfc in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
hi in college and watched some YouTube videos and read up on things I think I got the right formula but I'm not sure. Zsc= Zesc(or Zdbsc) +...
Hi, and thank you to anyone who's taking the time to read my question. i'm struggling with the outcome of an adiabatic equation i'm doing and...
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...
My brain has been exercised a bit by this. Am I on the right lines with this extremely simplified example: If we take: -TNCS installation with a...
4K