andyww

Following an install we carried out in February that tested fine when complete, we have returned (finally) to commission the installation and on retesting are getting a strange reading on a light circuit: (bearing in mind, in the intervening 6 months, builders have been in and refurbed the flat)On a new lighting circuit, R1 & R2 test produces this result: with the light switch on reading is 0.18, with the light switch off it still reads 0.78
Switching is in a JB and to my mind with the switch off it should show open circuit - but we are getting continuity at 0.78

Anyone got any suggestions?
 
Following an install we carried out in February that tested fine when complete, we have returned (finally) to commission the installation and on retesting are getting a strange reading on a light circuit: (bearing in mind, in the intervening 6 months, builders have been in and refurbed the flat)On a new lighting circuit, R1 & R2 test produces this result: with the light switch on reading is 0.18, with the light switch off it still reads 0.78
Switching is in a JB and to my mind with the switch off it should show open circuit - but we are getting continuity at 0.78

Anyone got any suggestions?

Check the wiring between the switch and the light. I seems that there may be a short circuit in this section perhaps caused during the building work. Also, check the switch wiring.
 
Following an install we carried out in February that tested fine when complete, we have returned (finally) to commission the installation and on retesting are getting a strange reading on a light circuit: (bearing in mind, in the intervening 6 months, builders have been in and refurbed the flat)On a new lighting circuit, R1 & R2 test produces this result: with the light switch on reading is 0.18, with the light switch off it still reads 0.78
Switching is in a JB and to my mind with the switch off it should show open circuit - but we are getting continuity at 0.78

Anyone got any suggestions?

Remove all lamps and transformers if fitted. Remove any links installed for testing and perform a 500V IR test between all conductors with switch off then perform again with switch on. This should determine whether or not you have a fault in you cable.
 
Thanks all - it was actually a screw through the plasterboard straight into a cable - Thanks builders!
 

Reply to R1 & R2 on light circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock