on a pme system wre a rod is used to seperate metal parts from pme terminal how would you record r1+r2 of cpc conected to rod and r1+r2 of cpc conected to pme terminal ie swa


got some external lighting in midle of a lawn wired in swa and armer is continious but seperated from fitting metal work so that swa will have a good earth loop reading
earth conductive part of lighting is conected to 3 rods spead around circuit via 3rd core of swa so as to seperate from pme terminal but the circuit will have rcd protection at the main intake so r1+r2 of swa and r1+r2 of lighting circuit on the rod can not be recorded together as they are seperate
 
Dont quite understand what your saying, but the supply authorities seriously frown upon you using a pme system out side the equipotential zone. therefore you should have created a seperate tt system for what ever you are supplying outdoors. You only need verify your Ra and/ or R2.
 
Dont quite understand what your saying, but the supply authorities seriously frown upon you using a pme system out side the equipotential zone. therefore you should have created a seperate tt system for what ever you are supplying outdoors. You only need verify your Ra and/ or R2.
the system will be t.t as 3rd core of swa is seperated from pme and attached to a rod
 

Reply to r1+r2 reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hello, Hoping to get some advice on R1 + R2 radial testing and best practise. When doing R1 R2 instead of taking cables from mcbs/rcbos and the...
Replies
1
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock