R

RichardMoore

I've read about these circuit sand came across one today on a periodic (eicr) in a kitchen the spark has taken a 6mm into a 45a isolator and run a ring out on the load side to all the appliances. 60898 b32 rcd protected. In good condition to. Suppose it's not illegal it's out there!! rang the Niceic tech line and they explained the detail. So just wondering what people thoughts are on this circuit have you ever installed one and have any of you got issues with them eicr as in a observation sense?????
 
Generally called a lolipop and if installed correctly there is not a problem.
 
wonder how many would just fail em though sintra...just off the cuff `caus it wasn`t the norm`?...lol

Probable a large percentage lol. IMO it's down to the lack of education and understanding dished out these days. Saw one installation given a code 1 just because it was done in a T&E ring in the roof space with a JB spur to every socket. Wanted to charge the old dear £1500 to rewire a few sockets. :24:
 
I know that what threw me at first but there legal and not very well known really
look, what its all going to hinge on here is that CCC and VD of cable is compliant, that its in prescribed zones, that IR is good and that it meets disconnection times.
theres also sometimes the issue with inaccessable joints....but not the case here...
if its an ECR then note it...no code (as long as it passes visual + tests)...
 
Probable a large percentage lol. IMO it's down to the lack of education and understanding dished out these days. Saw one installation given a code 1 just because it was done in a T&E ring in the roof space with a JB spur to every socket. Wanted to charge the old dead £1500 to rewire a few sockets. :24:
pathetic innit...lol
 
pathetic innit...lol

Same as these muppets that see a 3036 fuse or a 1361 and quote for a rewire. :)

Sometimes you wonder why this trade is getting a bad reputation :(
 

Reply to radial ring hybrid circuit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K
I'm in the process of renovating a house. As I go through room by room I am removing old plaster and as the cables are exposed at this point I...
Replies
14
Views
3K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi. I have a radial circuit supplying electricity to the garage (part of the house). It's on a 20amp breaker, uses 2.5mm cable. It currently only...
Replies
67
Views
9K
I am not a qualified electrician, I was employed as an electrician after my MoD electronics apprenticeship but that was 30 odd years ago. So I...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock