by who the fairys wispering in your ear at night .Been asked a few times
Hey, the only thing fairies whisper in my ears is how good Buzz --- is.Ramp testing an MCB, yes you can get one ,but you need to get for one china ,lol.
[automerge]1576703225[/automerge]
by who the fairys wispering in your ear at night .
Yes, it's standard with protection equipment for the higher voltages or for very large or important lv installations (eg Southampton air traffic control centre - some years ago now!).
Although ramp testing is not the thing to do.
You usually test straight forward overcurrent equipment at 2x, 5x and 10x, in addition if it has instantaneous trip (which mcbs do) 1.2x that value. (and adjust the 10x down if needs be)
Basically you prove the characteristic trip curve.
If you are testing protection relays, these have a rating of 1 or 5A, so 30x could be 30 or 150A
The standard unit I use is a sverker - which is 100A (and includes timer etc)
Alternative is a pte from smc
For higher currents or primary injection testing, I use a CSU - which is good for 600A
If you need more than this an ingvar does around 2000A
The most common ones do tend to be megger, but smc, abb, cee and many others make kit that can do it.
How much would a device cost to 6-63A MCBs?
It's nearly panto. season, so: Oh no it isn't!No product that I know of.
Lots of boiling kettles and a clamp meter?
I think if it says 32A then it’s pretty well definite it will trip at 32. Batch tested at the factory.
Not sure - I think a programma sverker 650 which will do 100A is £6k, and the sverker 750 or 780 is around £11k - it's good to 250A on it's own (add a CSU and it's up to 6000A)
But it's around £200 or so a week to hire
The pte is around the same price, but would be simpler than the 750/780
Nice safe joints you have made there Mate,A while back I made the WilkoSverk1000 that sort of does this... Well it was cheap anyway. The main ingredient is a transformer from an old microwave. Kept the transformer 230V primary, removed the HV secondary and replaced it with a turn or two of 10mm and got up to a couple of hundred Amps at a couple of Volts (from memory). Load current is tuned with the pliers, ha. I’d like a Variac from Santa to give it that pro look, but I understand he’s busy .
View attachment 54724
Now that's closer my budget, do you do one in blue?A while back I made the WilkoSverk1000 that sort of does this... Well it was cheap anyway. The main ingredient is a transformer from an old microwave. Kept the transformer 230V primary, removed the HV secondary and replaced it with a turn or two of 10mm and got up to a couple of hundred Amps at a couple of Volts (from memory). Load current is tuned with the pliers, ha. I’d like a Variac from Santa to give it that pro look, but I understand he’s busy .
View attachment 54724
Also remeber skipping about 40 Variacs in the late 90s when clearing a pilot plant at UMIST.A while back I made the WilkoSverk1000 that sort of does this... Well it was cheap anyway. The main ingredient is a transformer from an old microwave. Kept the transformer 230V primary, removed the HV secondary and replaced it with a turn or two of 10mm and got up to a couple of hundred Amps at a couple of Volts (from memory). Load current is tuned with the pliers, ha. I’d like a Variac from Santa to give it that pro look, but I understand he’s busy .
View attachment 54724
Righto, i'll have wait till next weeks overtime comes in then.
For an extra £99.99 I’ll paint it any colour .Now that's closer my budget, do you do one in blue?
Did get any reliable results from it?