Crosswire
I've admitted I was wrong, but I erred on the side of caution. I would rather be overly cautious than not cautious enough. Still thanks to this thread I will shave many minutes off my testing
Discuss RCBO 5In trip times. in the UK Electrical Forum area at ElectriciansForums.net
I've admitted I was wrong, but I erred on the side of caution. I would rather be overly cautious than not cautious enough. Still thanks to this thread I will shave many minutes off my testing
No probs with asking jimmy lol.
The rcd manufacturers recommend testing of the devices in this way for a start.
Plus the test is just to acertain the trip time of the rcd , so theres no need for any other part of circuit to be connected.
And finally , electronic gizmo's can interfere with the readings , as shown by ste macs query.
So you had the info all along and didnt bother to follow it ????
Then you claim my explainations were unclear in a completely ungrateful manner after i spent over an hour on the thread ???
Now youre still reluctant to do the testing as advised even though its alot quicker and easier just because you dont understand the science behind it ???
You're just all over the place to be honest.
Biff your tall on knowledge and frankly short on manners, and this is exactly what ****es people off, you clearly are an educated spark so WTF do you need to antagonise people ?..You have the knowledge base so use it to educate matey. I dunno if you get a kick out the wind up..but it's not an attractive trait, I say again you are clearly talented, so wind your neck in and see what is in front of you
J
and just a reminder..Just installing a new consumer unit for a customer. Split load board with 1 half RCD & the other half RCBO's. RCD & all but 1 RCBO has had good trip times, all sub 40ms at 1In & 5In, but the 6A RCBO for the kitchen lighting circuit is tripping at 40.8ms & 40.7ms at 5In. If I disconnect the outgoing live & retest the the trip times are 18.5 & 17.2. Anyone shed any light as to why this is happening & is it acceptable to test the RCBO without the outgoing ways connected?
wrong...i test RCDs by plugging in at a convenient socket. why? because it's easier. however, if i get unacceptable results, i'll then test at CU with circuit disconnected. on a new install. i'd test at CU before connecting circuits. all down to whatever takes the least time.
and its 1-0 to the Glennster...lol...I'm guessing that Tel meant whatever takes the least time to do.