1) In order for an RCBO to comply with BS EN 61009, the RCBO does not have to have a separate (functional) earth connection. However, the standard specifies that an RCBO which has a separate earth connection must behave in a certain way to conform to the specification, but the separate earth connection is not mandatory. There are RCBOs currently available that do not have a separate earth connection, yet they achieve full compliance and conformity with the standard.

2) The functional earth is used as reference by the internal RCBO electronics to increase the sensitivity, speed of operation and allows the device to detect an earth fault even if the neutral becomes disconnected. Losing the neutral connection is rare event, especially in TN systems that are increasingly common today. The probability of losing the neutral and having an earth fault at the same time, a double fault condition, is statistically small and evaluated by some manufacturers as so small not be of significance when specifying protection devices. In spite of this, there are those who advocate fitting an RCBO with separate earth connection “just to be on the safe side”. The penalties for this theoretical risk are RCBOs with taller form factors and the extra connection which make consumer units and distribution boards cramped and harder to wire, pushing up required connection time and costs. Even worse some electricians don’t know how to terminate RCBOs and it is quite common to find RCBOs with the functional earth connections cut off, this is clearly bad practice for a device where the electronics relies on a earth reference for its sensitivity and speed of operation.

3) Most manufacturers of RCBOs with functional earth fly-leads insist that these leads must be disconnected during insulation testing to avoid damage to the sensitive electronics, and during earth impedance loop testing to avoid misleading results. A minority of manufacturers insist on the disconnection of the neutral fly-lead during testing in addition to the functional earth, it is therefore important to consult manufacturers instructions before testing. Removing and replacing connections adds to the time and cost of testing, however, there are other issues. First, there is the possibility of failing to reconnect the functional earth fly-lead, leaving the device operating under conditions other than those for which is was designed. Secondly, disconnecting fly-leads goes against one of the basic principles of installation testing, which is that the installation should be tested in the exactly the same state as it will be operated in service. However, we often break this aspiration in installation testing.
 

Reply to RCBO earth reference tail in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
1
Views
227
Evening all . Just a quick question what do you guys typically charge for an rcbo spd consumer unit change 14 way . 10/11 rcbos few spare ways ...
Replies
25
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
692
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Last week I took the opportunity of having the mains power off to test the RCBOs in a Wylex Consumer Unit, fitted nearly 5 years ago, which has...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock