Hi all
I've just had 7 crabtree star breaker type a rcbos fail the half time on 180. I ordered replacements but they are the same tripping around 75ms. Just wondered if any one else was experiencing the same thing, it's only on the 6a rcbos. Making me doubt my tester tbh
Many thanks
 
The tripping current of the MCB part of the device will have no bearing on the RCD test time, or more precisely, should not.

Can you clarify whether the 75ms is for 1x the rated trip current (30mA) or 5x (150mA).
 
I have had an issue lately with another brand of RCBO.

Testing advice given to me by the manufacturer was to ensure

Batteries were fully charged
Tester recently calibrated
Correct setting on tester selected
Loads removed and circuits disconnected
To try another tester to rule things out.
 
He did say Half...

Yeah, but what does "half time on 180" mean exactly? If it's half I, then the 0 or 180 part is meaningless because the half I test spans multiple cycles. In which case, is it 'they are failing half the time on 180'? In which case, we need to know the test current to establish whether 75ms is in fact a fail or not.
 
Can you try your tester on another rcbo, to rule it out?
all of the other rcbos in the board tested out fine just the 6 amps
[automerge]1580839565[/automerge]
I have had an issue lately with another brand of RCBO.

Testing advice given to me by the manufacturer was to ensure

Batteries were fully charged
Tester recently calibrated
Correct setting on tester selected
Loads removed and circuits disconnected
To try another tester to rule things out.
i shall try replacing the batteries. just thrown me out a bit because all the others passed, but i cant imagine there being so many manufacture faults
 
Try doing a ramp test on the devices and see how many mA causes them to trip. I take it you have your meter set to test type A and not type AC.
 
I have had an issue lately with another brand of RCBO.

Testing advice given to me by the manufacturer was to ensure

Batteries were fully charged
Tester recently calibrated
Correct setting on tester selected
Loads removed and circuits disconnected
To try another tester to rule things out.
Awesome advice given there by the manufacturer Andy, bet you could never had thought of them.
 
Yeah, but what does "half time on 180" mean exactly? If it's half I, then the 0 or 180 part is meaningless because the half I test spans multiple cycles. In which case, is it 'they are failing half the time on 180'? In which case, we need to know the test current to establish whether 75ms is in fact a fail or not.

Excuse my ignorance SC.. I am drunk as officially from today I am divorced! Amicably though which is good..!

But half is surely half i.e. 15mA is the test current if the test equipment is doing its thang correctly ...and it should not be tripping whether it be a B6 or a B40... Basically they should not be tripping..I feel I may be missing something as you are always on the ball and knowledgeable...
 
Excuse my ignorance SC.. I am drunk as officially from today I am divorced! Amicably though which is good..!

But half is surely half i.e. 15mA is the test current if the test equipment is doing its thang correctly ...and it should not be tripping whether it be a B6 or a B40... Basically they should not be tripping..I feel I may be missing something as you are always on the ball and knowledgeable...

You're not missing anything, when I first read it I just felt that a little clarification may help expedite some responses. Clearly I was wrong as most people seem to have interpreted it in the manner in which it was intended (I draw this conclusion as the OP hasn't provided any clarification) :)

Congrats/Comiserations on the divorce (delete as appropriate) :)
 

Reply to Rcbo failure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
705
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
711
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
89
Views
3K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
868
I have an electric oven - now many years old. I have replaced the main circular 2.5kW oven element (ELEHY6708) several times over the years...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock