Hi there, i have recently wired a lighting circuit and a radial circuit for two socket outlets. Run the feeds for both circuits using a 5 core 2.5mm high tough cable from the distribution board to a jointbox. From the j/b i took my feed for lights and feed for sockets, used same earth for both circuits. Lighting circuit is on a 10a mcb and radial for sockets is on a 20a rcbo.
Completed wiring everything worked fine until i hit test button on rcbo and found it would not reset. Only when i switched off the 10a mcb for lighting circuit would the rcbo reset, found this very strange! Have tried different rcbo, but same thing happens, checked all wiring everything looks ok. I know using the same earth for both circuits is not ideal but can't see how it could effect the test button. Really not sure about this one any advice would be welcome.
 
Is your wiring method acceptable to BS7671?? I can't see how it can be, as you need to isolate 2 separate OCPD to isolate this cable.

I'm pretty sure his wiring method is acceptable Eng, see Section 521.7.

Hi there, i have recently wired a lighting circuit and a radial circuit for two socket outlets. Run the feeds for both circuits using a 5 core 2.5mm high tough cable from the distribution board to a jointbox. From the j/b i took my feed for lights and feed for sockets, used same earth for both circuits. Lighting circuit is on a 10a mcb and radial for sockets is on a 20a rcbo.
Completed wiring everything worked fine until i hit test button on rcbo and found it would not reset. Only when i switched off the 10a mcb for lighting circuit would the rcbo reset, found this very strange! Have tried different rcbo, but same thing happens, checked all wiring everything looks ok. I know using the same earth for both circuits is not ideal but can't see how it could effect the test button. Really not sure about this one any advice would be welcome.

Firstly, you need to check, check, then triple check that your neutrals are not crossed over at any point throughout the circuit/s. My bet is that they are and you've missed it.

Secondly, I'm assuming you've done your testing? What were your results for the two circuits?
 
Hi there thanks for your reply. Have checked wiring many times definitely ok. Done an insulation resistance test and all results were fine. Problem is with test button not closing after operation, you would think there is a fault on the cable but there can't be as surely rcbo would be tripping out all the time. Hate not knowing what is causing it, if you can think of anything else let me know, thanks again.
 
Not that I can immediately think it's relevant, but what's the earthing arrangement?
 
I hope not to offend with this question - Is the RCBO wired correctly? Easy to forget and put the circuit neutral into the neutral bar instead of into the RCBO. That could cause this to happen. Whenever I have come across instantaneous RCD or RCBO operation in relation to another circuit being swtiched on, it has always been neutrals related (if my memory serves me correctly - not always the case).

Best of luck
 
Probably worth checking the individual sockets. Take each faceplate off and disconnect. Then run an IR test between each of the terminals.

I only suggest this as I once had a similar problem with an RCD not setting on a newly installed 20A radial. After hours of head scratching it turned out it was a faulty socket outlet!
 
I hope not to offend with this question - Is the RCBO wired correctly? Easy to forget and put the circuit neutral into the neutral bar instead of into the RCBO. That could cause this to happen. Whenever I have come across instantaneous RCD or RCBO operation in relation to another circuit being swtiched on, it has always been neutrals related (if my memory serves me correctly - not always the case).

Best of luck

Dammit, I just thought of that but you beat me to it! :D
 
Head scracter.

If your dead tests are good

Does the RCBO test OK at 5 & 1 times.

When you do switch on the RCBO and then the lighting cct I take it that the RCBO does not see a imbalance. I take it you have switched the lights on and off and tested a load on the sockets making sure it holds?
 
Are there any other existing circuits on the board that you have put these on? If so, have you tested IR on these circuits? I know that it shouldn't be relevant but RCBOs are only single pole, any N - E short could be causing it to behave strangley. Maybe clutching at straws here............but it's worth a look.
 
As it's a TT system, I'm guessing the MCB is covered by it's own RCD. Are you 100% certain the RCBO hasn't been installed in some way incorporating the RCD's neutral supply?
Is the RCBO neutral completely independant of the MCB (RCD) neutral?
 

Reply to rcbo only resets when other mcb is off in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a 6amp RCBO feeding a 2.5mm radial ( temporary measure) It tripped, as I expected would But once tripped, all the other circuits went...
Replies
25
Views
2K
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...
Replies
7
Views
781
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
538
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock