Discuss RCBO question. in the Australia area at ElectriciansForums.net
tigerpaul
Had a strange one the other day.
I was in a main switch room and had an RCBO connected into a DB, but switched off. From it was a radial in singles to a socket adjacent to the DB. The conductors were disconnected at the socket, if I touched the neutral down to earth, it sparked as though it was live, and the Main LV panel behind me started to hum.
Why was this happening?
A photo might help. If there was a flash between the neutral and earth then either the neutral is floating at a voltage wrt earth or the earth isn't actually at 0 volts. The RCBO doesn't appear to be providing isolation possibly either.
Sounds like it might be a good time to drag out the testers before it nails some other poor soul.
Ok I forgot to mention, when I tested it I had 0v between L and E, but 2v between N and E.
The RCBO was in the off position when this was happening.
BTW, all live tests passed.
TN-S
I'd have thought that with the RCBO switched off, there would not be any possibility of any potential difference between L N or E. Evidently not in this case.
Reply to RCBO question. in the Australia area at ElectriciansForums.net
So I had an inquiry to make an electric panel (single phase) with RCBO, but it seems like our customer uses type C and F power plug (I live in...
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Hi guys, We’ve had a new CNC Machine from China arrive this week. It came with a monitor and a tower to run the software. The monitor and tower...