Discuss RCBO socket circuit tripping. in the UK Electrical Forum area at ElectriciansForums.net
GBDamo
I'm stuck here fellas.
I have a radial with only one double socket outlet in 2.5mm T&E on a 20A RCBO running five meters in surface mounted trunking. TN-S, R1 and R2 good, 243V measured, Ze 0.12, Zdb 0.29, Zs 0.36, IR all +200MOhms.
RCD trip tests all ok at 0 and 180 and ramp 24mA.
Now these sockets are only used for one thing, two 580W water distillers.
Both have been clamped during operation and are drawing 2.4-2.6A as expected.
Both have been IR tested L-E & N-E and +200MOhms.
I am stumped to the point where I may run in a new socket on a new RCBO, cost not an issue the customer just wants it stopped.
My concern is the issue could be with one or both the distillers units and not the circuit.
I don't have a low current clamp meter so cannot measure earth leakage directly.
Any ideas where to look next, I'm still on the job by the way.
First thoughts are towards faulty distillers..
Have you tried plugging in other appliances?
I'm leaning that way too but cannot think of any definitive way of proving it.
I think it's happening when there thermal overload kicks in, i.e. when they're run dry as they often trip overnight.
I don't want to test that as it may damage the kit but it's the only theory I have at the moment.
I think the customer knows this as they have had them put on a dedicated circuit so as not to take down other areas.
Most likely faulty appliance. How often is it tripping, instantly or randomly? Seen something like this before even though it recently "passed" all its PAT tests. As above swap rcbo for mcb and replace socket for T earth and mark up.
Defiantly points to a faulty appliance. A PAT wouldn't necessarily pick this up though, the equipment is likely 'safe' to pass PAT. Could be worth contacting the appliance manufacture.
Turn them off overnight and see what happens.
Just passed PAT test..:D
Nothing wrong with removing sealed plugs, happens all the time with washing machines, etc.
Are the units easily serviceable?
Do they have spare parts?
Reply to RCBO socket circuit tripping. in the UK Electrical Forum area at ElectriciansForums.net
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...