Evening All...I've not posted in a while which is a good thing as I can now work most things out myself!!

Just a bit of help needed with this one though!!

I have two consumer units, both have a mixture of MCB's and RCBO's on one of the consumer units the RCBO's are tripping randomly (The customer is adamant that it's since the smart meter was installed but probably coincidence),

I have done an IR test on the circuits with the RCBO's and they all pass. I didn't have time to test all the other circuits today but will do next time.

My question really is..would a N to E fault on the non-RCD circuits cause the RCBO to trip?

I'm just wanting a bit of info to go back with tomorrow as they customers are OAP's and they have had sparks look at it the past and not sorted it.

Cheere
 

James

-
Mentor
Esteemed
Arms
Supporter
Patron
Reaction score
5,580
A N to E fault could cause the issues you are having.
it is the most likely fault unless of course the smart meter is within a foot (300mm) of the distribution board and then all bets are off!
 

timhoward

-
Esteemed
Arms
Reaction score
3,948
My question really is..would a N to E fault on the non-RCD circuits cause the RCBO to trip?
No. An RCBO should only trip if there is leakage downstream of it on that circuit.
Remember the N bar is upstream from the RCBO. The circuits return N current path has to pass through the RCBO first , so the RCBO will be balanced, and won't notice any upstream N-E fault.

So circuits not on RCBOs with N-E faults should not normally affect RCBOs.
If upstream N-E faults tripped RCBO's then if you think about it every TNCS setup would have a problem.

In this case I'd quickly test the other circuits, and then believe the customer, as smart meters can most certainly cause this problem.
What make CU is it?
 

marconi

-
Mentor
Esteemed
Arms
Reaction score
3,461
A thought. Do the RCBOs have a functional earth? Some RCBOs use the FE to monitor N-E voltage and if it rises above a threshold they trip because it 'thinks' the supply side N has become open circuit. Check then the goodness of up stream N and E conductor connections and indeed the functional earth connections. This could tie in with the client's observation about it all starting after the smart meter was installed.
 
OP
D
Reaction score
38
No. An RCBO should only trip if there is leakage downstream of it on that circuit.
Remember the N bar is upstream from the RCBO. The circuits return N current path has to pass through the RCBO first , so the RCBO will be balanced, and won't notice any upstream N-E fault.

So circuits not on RCBOs with N-E faults should not normally affect RCBOs.
If upstream N-E faults tripped RCBO's then if you think about it every TNCS setup would have a problem.

In this case I'd quickly test the other circuits, and then believe the customer, as smart meters can most certainly cause this problem.
What make CU is it?
Hi thanks for the advice, it's a Hager CU.
 

Reply to RCBO tripping advice. in the Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have an RCBO that keeps tripping. It is a new install to feed an EV charger with an isolation switch between and is around 5 foot from the...
Replies
1
Views
196
  • Locked
Hi all I am in an industrial unit and the 100mA RCCB keeps tripping. They use it as the main switch inside of the unit's distribution board. The...
Replies
41
Views
1K
Hello, Firstly, I'm aware other people have posted similar topics on this forum, I'm not trying to create a duplicate, but more looking for...
Replies
5
Views
446
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
698
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
13
Views
1K

New Posts (Please Reply)

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Top