Hi guys,
am I missing something obvious? Hager 40amp type B RCBO supplying a 9kw shower (actually pulling 36 amps). Whilst shower is on, no matter for how long/short, everything is ok. However after it is switched off the RCBO trips - this is not immediately, it can happen an hour or two, or even longer after. Cable insulation tests fine, all connections (shower, switch, board) good, Zs fine. Only the shower on the circuit. RCBO ramps at 27ma.

I appreciate that the rating of the RCBO is technically too low and a 45 amp would be better, but I can't see this being an overload issue given when the tripping occurs.

As I started, what if anything am I missing?

Regards.
 
i would check and re check the insulation if you have a intermitant N to E fault it could well cause the RCBO to trip, especially if there is supplimentary bonding going back from the lighting circuit to the shower switch ,ensure the switch polarity is right neons not on all the time , also check the Ze as supply faults can also trip an RCBO just a thought as for the breaker size you probably will not have a problem with it tripping my 10.8 kw shower is on a 40 amp MCB its never tripped in the 4 years its been in
 
Have you checked the current it is pulling and the earth leakage to see which is tripping.

Is there a high resistance fault in the isolator switch that is pulling 50 amps or so when off?

Is there water leaking into the shower body and slowly reaching the power supply?

Is it switched off at the isolator or just at the shower?
 
Have you tried IR testing the shower when its on and off?

It does not sound like a over current unless something is drawing large current when it switches off - doubt it.

How new/old is the shower? could a little bit of water of got into it which only crosses contacts when it is being turned off?

other option if you think it might be over current (or to eliminate it) change the RCBO to a MCB of same rating and try that - again I doubt it is an over current
 
All, thanks for the ideas and feedback. Sorry for the delay in responding, kept loosing my internet connection last night.
Shower is a Mira, not sure how old but looks to be in good nick.
No evidence of water pen or internal leaking.
Earthing is a good TNS, no supp bonding.
Interestingly, the isolator (MK 50 amp pull cord) had been getting left on as "it was stiff to operate". I've since changed this like for like and I don't actually know if the tripping has occurred since then - I'll check, 'cos you've got me thinking about the neon!
Have not tried changing the RCBO yet (don't carry these as spares due to the cost - I know, I'm a tight arse!).
Did not check the earth leakage given when the tripping occurs, but I will do if the problem persists.
Thanks again for the feedback - as always, food for thought!
 

Reply to RCBO tripping - any thoughts in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I will start with apologies, as I have not thought this through very much (at all) yet and have just sat down with a beer.... meaning I thought...
Replies
3
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Recently my RCCB keeps keeps tripping intermittently. It can happen between several hours to few days when a trip will occur. During the trips, no...
Replies
35
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock