Discuss RCBO trips different RCBO in the UK Electrical Forum area at ElectriciansForums.net
I've just change a CU and installed RCBO's. There is a 32a SP RCBO suppling a ring final circuit. There is a 6a SP RCBO radial lighting circuit. When the 6a radial circuit is energised the 32a RCBO trips. With the 6a dead the 32a stays in.
I expected to find a shared neutral but there is no continuity between the neutrals and no continuity between the lives.
Hi - as per Charlie, I suspect the two circuits are connected :) .
Thats what I thought but I get infinate continuity between line of 6a and line of 32a. Infinite continuity between neutral of 6a and neutral of 32a. I also tested between line of 6a and neutral of 32a, and between line of 32a and neutral of 6a with same results.
Hi guys, well I'm back looking at this issue again. I cannot prove a shared neutral no matter what test I run but have found some weird ---- going on. With all light switches off both circuits will stay in but switch a light on and sometimes the 32a will trip sometimes it stays in, it will usually trip when I switch on a second but it doesn'tseem to matter which lights I pick. If I press the test button on any of the other 8 RCBO'S the 32a RCBO in question trips as well. Also when I arrived the 32a had tripped over night.
Hi guys, well I'm back looking at this issue again. I cannot prove a shared neutral no matter what test I run but have found some weird **** going on. With all light switches off both circuits will stay in but switch a light on and sometimes the 32a will trip sometimes it stays in, it will usually trip when I switch on a second but it doesn'tseem to matter which lights I pick. If I press the test button on any of the other 8 RCBO'S the 32a RCBO in question trips as well. Also when I arrived the 32a had tripped over night.
What tests have you conducted? I cannot access your profile, so we cant ascertain what if any experience or qualifications in the electrical field you hold, so it makes it doubly difficult to tailor any advice or answers, telling you to get an electrician in would be crass unless we know your limitations.
I'm got my inspection and testing tickets. I've done all the standard tests as well as loads of continuity test between the different circuits (neutral to neutral, etc) I also did a insulation resistance between the neutrals, achieving a reading of 185M ohms.
It did just trip when I energised a third circuit.
As Strima said check for loose neutrals,
Another favorite when people change boards for split phase CUs are having the neautrals on the wrong neutral links as they only trip when start adding load to them. The number of my sparky freinds that call me with this problem
If not this then Have you done IR test between the neutrals and the CPCs of the affected circiuts, i have had it before where a voltage exceeding 50 volts has been present on the CPC of a circuit that wasnt even connected and when all connected in to new RCD loaded CU has identified the problem thet as the custer tries to say "There wasnt a problem before you touched it" errm "yes it was its just RCDs will find issues no previously apparent"
:mad:
Reply to RCBO trips different RCBO in the UK Electrical Forum area at ElectriciansForums.net
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
I had a 6amp RCBO feeding a 2.5mm radial ( temporary measure) It tripped, as I expected would But once tripped, all the other circuits went...
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...