( 1 ) What would cuase a consumer unit, with RCBOs installed, to all trip out at virtually the same time, at about 7am every morning, but at no other time ?

It's a TT earthing system, with overhead supply cables linking the house to the pylon in the street. Then two cloth covered live tails from there to the main head. These rae the original cables and have been around since the beginning of time.

Could it be a fault with one of the LIVE conductors that link to the house from outside ?

The elecy board have had a look and are going to replace the two cloth cables with a new concentric cable ( like those used for PME connections ). All the circuits have been tested, and given the thumbs up. All RCBOs function correctly and in the correct operating times.

The elec board tested at the board. My tested Ze was 2.59ohms. They obtained a similar value, and concluded that it was far too big. For a TT supply, I reckon that's pretty darn great !!!!!!

( 2 ) Can I refuse to have a TNCS connection ( and request that no earth connection is provided ) and continue to use the earth electrode ????
 
The elec board tested at the board. My tested Ze was 2.59ohms. They obtained a similar value, and concluded that it was far too big. For a TT supply, I reckon that's pretty darn great !!!!!!

Your electricity board man seems not to have read the rules. for a TT system with RCD on all circuits the maximum Ze is calculated so that your earthed metalwork doesnt go over 50 volts while the RCD is being tripped by a fault, thus Ze is less than 50 volts/ 30 milliamps = 1666 Ohms. The regs does point out, though, that if your Ze is actually over 1Kohm then it is probably pretty unstable and you should get a longer or wetter earth spike.
 
just a few bits to think about

-have had rcd's trip in next property before on test, tt supplys
-on peak switches about 7 am earth leakage.
-rcbo in lower amps trip under zs test more often.tt supplys
-your live neutral zs not rod resistance under 0.35 get pme may stop tripping.
 
Last edited by a moderator:

Reply to RCBOs . . . all tripping at same time. in the Australia area at ElectriciansForums.net

Similar Threads

I was recently called to a domestic nuisance tripping job, dual-RCD Wylex board with one of the RCCBs tripping intermittently, mostly during the...
Replies
25
Views
6K
My garden lighting was tripping my MCB so I checked all the junction boxes outside. I disconnected the live, neutral and earth connections in...
Replies
2
Views
863
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
Hi Ive looked around and i cant see this particular scenario being discussed. I think i may have been a numpty, but bear with me. I have just...
Replies
16
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock