Excuse my ignorance,can someone explain to me the problems of using RCBO's on a TT system,and whether and why its unsafe
Discuss RCBO's on TT system in the UK Electrical Forum area at ElectriciansForums.net
No problem at all on a single phase TT supplied cu, so long as there is a DP main switch also in use on the CU.......have been fine on my assessments up to now.
The argument given by some is:
There is a requirement for DP disconnection for isolation purposes, the main switch covers this nicely.
A main switch will not clear a N>E fault
There is a requirement for all live conductors to be disconnected under fault conditions, the SP rcbo does this fine.
Others will argue (correctly) that the neutral is also a live conductor and as such should be disconnected in the event of a fault, a single pole rcbo does not achieve this.
On a three phase TT supply all three phases & neutral need to disconnect under fault conditions (not got regs to hand so cant give the number)
I think there are only a couple of companies that produce single module double pole rcbos at the moment, I predict there will be a few more companies selling them in the coming years.
PM sent with detailswho makes compact rcbo not clever