F

fylthespider

Hi all, new to the forum and got a cracker for you.
story so far...
100 year old mid terrace house. was asked to inspect/test 30year old wiring. turns out ok so recommend new cu, all rcbo's and DNO to install PME.
shower, kitchen rm, house rm, lights up and down.
all goes well, everybodys happy.

about a month later i get a call.... the dreaded nuisance tripping ARRGH!!!!

so, perform another full test and pat test all appliances and again, all good. insulation test good, no shared/crossed neutrals/earths etc.
so leave with instructions to keep a log of tripping.

after about a month i went back to find completely random tripping, any and all rcbo's in any combination at random times etc.

tested again and still no joy.

tried substituting mcb's in various combinations, isolated each circuit one at a time, all the usual tricks.
even had shower rcbo trip when outgoing cable isolated ?????.

starting to loose the will on this one.

any ideas ?
only thing i can think of is transients on the supply as its the only thing common to all rcbo's, but of coarse the DNO dont want to know.

I rate myself as a good sparky, been part p since it started, 2391 since 2001, Ive never been stumped before but this got me tearing my hair out (and i havnt got that much left)
only good thing is the customer is a friend so she's not dancing on my neck, but i got to figure this out cos its been going on for months.

any thoughts appreciated cos i'm ready to give up and get a job at tesco's.

cheers phil.
 
Hi all, new to the forum and got a cracker for you.
story so far...
100 year old mid terrace house. was asked to inspect/test 30year old wiring. turns out ok so recommend new cu, all rcbo's and DNO to install PME.
shower, kitchen rm, house rm, lights up and down.
all goes well, everybodys happy.

about a month later i get a call.... the dreaded nuisance tripping ARRGH!!!!

so, perform another full test and pat test all appliances and again, all good. insulation test good, no shared/crossed neutrals/earths etc.
so leave with instructions to keep a log of tripping.

after about a month i went back to find completely random tripping, any and all rcbo's in any combination at random times etc.

tested again and still no joy.

tried substituting mcb's in various combinations, isolated each circuit one at a time, all the usual tricks.
even had shower rcbo trip when outgoing cable isolated ?????.

starting to loose the will on this one.

any ideas ?
only thing i can think of is transients on the supply as its the only thing common to all rcbo's, but of coarse the DNO dont want to know.

I rate myself as a good sparky, been part p since it started, 2391 since 2001, Ive never been stumped before but this got me tearing my hair out (and i havnt got that much left)
only good thing is the customer is a friend so she's not dancing on my neck, but i got to figure this out cos its been going on for months.

any thoughts appreciated cos i'm ready to give up and get a job at tesco's.

cheers phil.

We had a callout to a day centre a few weeks back, RCBOs randomly tripping, rather similar to what you describe.

The weird bit was the caretaker saying that the problem always happened when the council were cutting the grass outside!

Anyway, it turns out that the DNO neutral meter connection (external supply) was loose and every time a decent load kicked in or a vibration took place outside, a few RCBOs would trip!

I was quite proud of that one but to be honest, if it wasn't for the caretaker mentioning the grass cutting, it would have taken a hell of a lot longer to find, especially as the neutral loop impedance reading was exactly as I would have expected!

Worth a shot anyway as it probably won't show up in your conventional testing regime!
 
We had a callout to a day centre a few weeks back, RCBOs randomly tripping, rather similar to what you describe.

The weird bit was the caretaker saying that the problem always happened when the council were cutting the grass outside!

Anyway, it turns out that the DNO neutral meter connection (external supply) was loose and every time a decent load kicked in or a vibration took place outside, a few RCBOs would trip!

I was quite proud of that one but to be honest, if it wasn't for the caretaker mentioning the grass cutting, it would have taken a hell of a lot longer to find, especially as the neutral loop impedance reading was exactly as I would have expected!

Worth a shot anyway as it probably won't show up in your conventional testing regime!
Classic, seen it on the main incommer and RCD connections but never on the DNO side, top marks for getting to the bottom of that one IQ!
 
definitly not the lawn mower, she got concrete back yard.
not got clamp meter, but left multi-meter (with max reading hold) inline with earth for couple hours and nowt. would like to leave it for couple days but wouldnt be very safe.
rcbo's from denmans, control gear i think. used loads of them in similar situations and no probs. all hold fine on 15ma test so i dont think it that.

i'd like the dno to monitor the line for a while but since it took 3 weeks for them to change a metal clad neutral fused head i dont think i'll have much luck there.

I thought about floating neutral but as IQ said, perfect neutral readings.

Any one used transient suppressors on incoming line?

getting tempted to do a rewire then shout at dno about compo, but need to be sure where the fault is first otherwise eggy face.

thanks for the replys tho.
 
As mentioned above but have you double checked connections in the incoming suppy such as the meter, fuse ,Henley blocks, main switch and that the rcbo's are not not clamping on the bus bar properly. Know they are simple ones but sometimes it's the simple ones we miss.
 
I had this once with one rcbo on a board I fitted turned out the N condutor copper bit sheard off and had enough of a contact to test ok, and to make it worse I had cut the pvc to short and the clamp had a hold of it so it felt tight, I only found it as I was replacinging it with a MCB as a temp mesasure,
Pict
 
I've had this before:- hallway landing floor joist notched out and packed with cables, floorboard pushing on the cables and pvc being worn away slowly over time. Random tripping? Going to the toilet at 2am stepping on the floorboard giving enough to trip rcd (in my case) but not a short circuit therefore mcb not tripping.
 
You have a recording meter set it to record N-E for a while. You say the DNO replaced the service head. There’s good chance it’s the culprit.
 
not done a ramp test but they do hold at 15 and 20 ma so dont think its the rcbos. had new incoming cable installed and all connections look ok and are tight.
been back to basics as yes, its often the simple stuff that gets you.

thing thats got me foxed is how can an rcbo trip when theres nothing connected to it???? ( the shower circuit)
Only thing its connected to is the incoming line and neutral. so, no current able to flow, yet still it trips.
which makes me think maybe some strange transient on the supply. dont know and think its time for a pint.

Thanks for the ideas tho.

cheers phil
 
I do not know the answer here so do not take this as necessarily correct, but from reading other threads on here there is a suggestion that some RCBOs can trip because of a large current flowing in an adjacent MCB/RCBO from induced current in the coil.
I would have thought that this would be addressed by manufacturers but you never know.
If possible it may be worth removing every other RCBO across the board and try the remaining circuits and see if they trip.
This would at least address the disconnected RCBOs tripping.
Might be worth a try.
Tell me to shut up if I am talking rubbish!
 
not done a ramp test but they do hold at 15 and 20 ma so dont think its the rcbos. had new incoming cable installed and all connections look ok and are tight.
been back to basics as yes, its often the simple stuff that gets you.

thing thats got me foxed is how can an rcbo trip when theres nothing connected to it???? ( the shower circuit)
Only thing its connected to is the incoming line and neutral. so, no current able to flow, yet still it trips.
which makes me think maybe some strange transient on the supply. dont know and think its time for a pint.

Thanks for the ideas tho.

cheers phil
Any chance of proving the RCBO at home (in a temp supply to a temporary board)?
 
already swapped the rcbo's from another job where they were fine, so im 99.9% sure its not the breakers. nice idea tho.

hmmm, magnetic cross talk. now that sounds possible, worth a try. might even try steel screen between the rcbos.
its another straw to clutch at lol.

cheers. will let you know.
 
already swapped the rcbo's from another job where they were fine, so im 99.9% sure its not the breakers. nice idea tho.

hmmm, magnetic cross talk. now that sounds possible, worth a try. might even try steel screen between the rcbos.
its another straw to clutch at lol.

cheers. will let you know.
What I was thinking is, if you can prove it in a temporary supply and it's fine, then you could take the temp supply to the premises and connect to the meter and use it to prove whether it's the DNO side or the house holders side (rather than having to take the sherlock approach and prove it's not the house side).
 

Reply to rcbo's tripping randomly in the Australia area at ElectriciansForums.net

Similar Threads

Hi All, Seeking some thoughts on my own Omega free standing 900mm oven. Over the past year the oven has been tripping the supplying RCBO unit. I...
Replies
2
Views
487
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Replies
26
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
711

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock