- Reaction score
- 3
after finding an unexpectedly high Zs on a shower, I narrowed it down to:
Zs at input of RCD (RCCB) is around 0.18 as would be expected but the Zs at the output of the RCD is 0.96! Both tests done with 3 lead low test on Megger MFT with 3 month calibration.
It is a split load board and both RCDs show similar results. Both pass standard TCD trip tests.
I haven't come across this before although some googling showed an MK article that said the electronics in an RCD can cause this.
It is a pain in the bum to have to bridge out the RCD to do the Zs tests in this case!?