Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will not pass the rcd test at 1 or 5 times, it fails to trip and my tester says time exceeded and shuts off.
Every thing appears correct I ran out of time so have isolated it the shower and will investigate it again tomorrow.

all advice would be appreciated.

thanks
 
1,How familiar are you with your test equipment 2, at what point in the circuit did you preform the tests on the RCD, 3 what do you mean you ran out of time, you should know by now electricians can make time lol
 
I'm familiar with my tester, I ran the test at both at the shower end of the circuit and the consumer unit end. I had to pack up due to child care issues otherwise I would have spent longer longer looking for the fault. To double check my tester I checked the properties other rcd using the socket tester and it worked as it should, so I'm certain my tester is ok. I was using the testers leads to test the shower circuit.

- - - Updated - - -

I checked tester was set to 30mA
 
Onions, thanks for that, that was what I was thinking, i was beginning to think I had missed something. But as the r1 and r2 and insulation tests are ok there shouldn't be a damage to the cable. I checked all connections were tight in both the shower and the switch unit.
 
The test button simply introduces an imbalance coil to test the mechanism is working, so this won't help. Just out of interest, before you return the unit, have you tried using the leads in exactly the same way on your known "good" RCD, or did you use the plug adaptor? Just a thought in case you had something connected incorrectly in this instance.
 
one thing to check is that you have not put your meter onto test a dc rcd i was having the same thing on a job took me bloody ages to realize.

dom
 
Onions, thanks for that, that was what I was thinking, i was beginning to think I had missed something. But as the r1 and r2 and insulation tests are ok there shouldn't be a damage to the cable. I checked all connections were tight in both the shower and the switch unit.

Zs test at shower would have confirmed your earth was good without the rechecking of all your connections (as you already done r1 & r2)

You said you checked the other RCD with the plug attachment - I would check both RCDs, at the board, with the leads - if one trips and the other doesn't then as Onions said......
 
Hi, I've been installing a new shower, using a shower consumer unit complete with rcd. All the tests passed, r1 And r2 were 0.23 ohms, insulation resistance was >299M ohms, polarity was correct. But when I test the rcd I cannot get it to trip. It passes when the test button is pressed but will not pass the rcd test at 1 or 5 times, it fails to trip and my tester says time exceeded and shuts off.
Every thing appears correct I ran out of time so have isolated it the shower and will investigate it again tomorrow.

all advice would be appreciated.

thanks
You have not mentioned ZS! I take it your shower unit has a ZE /Ra ?
 

Reply to Rcd fails test. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock