Hi all,
I have just read an old periodic report that has highlighted a TT system that has an RCD main switch mounted in a non insulated enclosure (metal) as a category 2.
Does it state anywhere in the reg that the RCD should be in an insulated (plastic) enclosure. I've had a look but cant find anything.
I would consider the origin as the outgoing terminals of the distributor’s meter or isolating switch, not always possible to have an RCD located here on the tails.
So therefore load side & connected tails of the dist meter would not be the origin, but would be classed as the customers equipment (as in not the origin) & this is where you would find the single rcd.
Your meter tails will comply if they are insulated & sheathed.....but will the enclosure they enter ?
Consider a class I enclosure & any fault between the origin & the terminals of the rcd (tails in contact with the earthed Class I enclosure), thats right due to the probable high Ze on a TT system will mean the rcd will not detect the fault & the suppliers cutout will not dissconnect the fault leaving the Class I enclosure and all earthed metalwork in the installation at..........................the supply voltage potential.
Class II enclosure or the insulated bushes that keep the tails seperated.
Hows that for you
Ok not clever, got it now thanks. That makes perfect sence. I just wish the regs were writen in english and not some strange language from a land far far away!!! Cheers.
Reply to RCD for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
5K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...