To "isolate it" from the house. 40A mcb in house, not rcd protected. SWA earthed at house. Earth pole/rod for garage. But then I do a lot of work out in the sticks.
but its TN eng.....so:Why would you leave behind a perfectly good earth with around a 0,35ohm Ze, for an earth rod, with 100 to 200 ohm Ra??
Either the OP can mount a small switch fuse, or MCB at the origin and supply the garage from that, providing a typical 2 way garage CU with RCD, or use his existing CU RCD protected MCB, and leave out the RCD at the garage CU. Nothing stopping the OP from also driving a decent sized/length Rod and connecting that in to the EMT, pretty pointless though if it has a high Ra value!!
Amlu
As there would be no discrimination between 2 X 30mA RCD's it would be anyone's guess which RCD device trips first (or both tripping). Ideally you don't want a garage fault to trip out half the house. There is only one way to overcome this, if using 2 X RCD's, that is by the use of a S type (time delayed) RCD upstream....
but its TN eng.....so:
if he does away with that crappy bit of 2.5 flat twin...and uses an armoured (full length)...he`s killin several birds...
1)its a Tn system....so no RCD at origin
2)no hidden joints...and you know what i think about them!!
now...the point here is this:
do you
a) RCD it at the house C/U end...and risk taking out half the house (as eng has quite rightly pointed out) or..
b) accept the extra work involved (replacing that 2.5 flat)...and run an armoured full length...thus allowing you to RCD the garage on its own...thereby not taking out circuits within the house (lighting on stairs maybe)....a better way...
see, he`s got the costs of a 100mA s type to consider here as well....yes i know that cost always comes secondary to safety & compliance.....but it will probably be cheaper to just get a new length of armourd pulled in or if the existing armoured is suitable (no damage and CSA)...then a scotchcast is another option (if the existing armoured is buried in the garden out to the garage..under grass maybe).....better than jointed on a throughbox...onto a stupid bit of flat twin..lol...I know it's a TN system, which is why i'm really suggesting he protects the origin with a fuse or unprotected MCB etc..., but if the OP just wants to install straight off an already protected way, then best not include an RCD at the garage.
Fully agree with your suggestion of SWA from the CU, and maybe converting his existing dual RCD CU to having an unprotected way. ...But as you say, is he prepared to go along with the bit more extra work involved?? lol!!
eh?....for them that don`t know maybe...lol...So, shoot me down in flames (if needed). I'm always willing to learn a bit more, or even the correct way. I've been lead to believe that extending TN-S is not good. TNC-S (PME) def frowned on. So supplying the out building at that distance is to make it TT.
Now if I've totally ballsed up my understanding of the situation, correction will be gratefully and gracefully received.
Mind you, when the garage is a 5 car + helicopter garage at the bottom of your "yard", I'd want it totally isolated from t'house.
So, shoot me down in flames (if needed). I'm always willing to learn a bit more, or even the correct way. I've been lead to believe that extending TN-S is not good. TNC-S (PME) def frowned on. So supplying the out building at that distance is to make it TT.
Now if I've totally ballsed up my understanding of the situation, correction will be gratefully and gracefully received.
Mind you, when the garage is a 5 car + helicopter garage at the bottom of your "yard", I'd want it totally isolated from t'house.
RCBO the garage supply that way only that one circuit will trip and no others.