Discuss RCD keeps tripping?? in the UK Electrical Forum area at ElectriciansForums.net

P

Paultrim123321

No, don't panic, this isn't a plea for help, just sympathy. Asked to check out a bungalow this morning, (friend of the wife) apparently the "big switch in the fuseboard keeps tripping?"

Oh well, turned up with the family in toe as I thought this won't take long. Old Wylex board with BS 4293 RCD main switch. 5 1/2 hours later!!:/ IR all circuits to find lighting radials neutral/earth very low! 1.4ohms to be precise, and no I don't mean 0.14mohms I mean 1.4ohms.
Well after some splitting/calculating/removing/more testing fault found at a bloody damaged neutral conductor in bulkhead light fitting in utility room, the sheathing was damaged on installation recently and was exposing inner copper conductors which where just touching the metallic reflector tray in the fitting. Repaired the damaged insulation all fine.
I didn't even charge them, felt guilty as they were in the eighties and i know another spark would have fleeced them for callouts and fault finding and probably even a new DB!
Oh well rant over.
 
Fair play to you Paul, that's the trouble with having upfront rcd protection, if it were a split db you would have found the fault more quickly.
 
Yeh I agree Dave. To be honest I quite enjoyed the challenge. My line of work means I have been carrying out Test and Inspection and design review work for a long time so to get my hands dirty so to speak was good, glad to know I still had 'it' though perhaps slightly slower than some of you guys:)
 
Nice geture Paul
icon14.png



Mind you, I like the line ( turned up with the family in toe )
Do you have big feet ?
icon7.png
 
Good work old bean, worked with this guy for a few years and did not know he could get his hands dirty,
Respect although I remember you telling me a few weeks ago you where fitting some new lights for a friend of the family coincidence ?????
 

Reply to RCD keeps tripping?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’ve a new self build house that I’ve moved into prior to the lockdown in the UK. 100amp supply from Scottish power. Within my Consumer Unit...
Replies
28
Views
4K
Hi all, Any help would by greatly appreciated as i have tried everything i possibly can. Heres some info on the situation, installed some spike...
Replies
18
Views
3K
The full blurb is below, but the TLDR is: RCD that tested perfectly (ramp test to 27mA can't remember the numbers for trip times but all was...
Replies
19
Views
2K
N
Hi , I'm a new member and resorted to joining this forum in an attempt to get to the bottom of a frustrating problem. I can see many forums where...
Replies
2
Views
2K
S
Hi all. This is my first post in the forums. I am almost at the end of my 3rd year at college, and don't yet own a multifunction tester so cannot...
Replies
13
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock