- Reaction score
- 29
Had a strange one today, hager 100a 30ma rcd failed to trip with the tester. TT earthing arrangement, also very strange readings. ze 197.4 ok normal for around that area the zs around 0.53. Went and got a replacement 80a 30ma rcd, the 100a was on the large side. Failed the test again. Went home pulled out the cupboard an older hager 80a 30ma rcd the ones that took up 4 module slots and it tested fine, all other circuits were disconnected. Can't see how it would be a neutral to earth fault unless I put the circuits back one at a time to see if one causes a problem...just not sure.