- Reaction score
- 8
Hi
Hopefully some can explain this perplexing issue
I'll try and explain the situation as best I can, hopefully its not to rambling -maybe its common knowledge but I'll bow to anyones supperior understanding
During an EICR checked test button RCD would not trip - checked with tester no trip on X1 or X5 so informed client it was faulty
Split load board 5 ways non RCD 2 ways RCD Hager Ze 0.20
however please refer to my very bad drawing attached.
Later on in testing - I switch off MCB A and rcd trips try to reset it cant do this unless MCB C is switched off then RCD will reset
MCB C put off RCD trips immediately
Live test with RCD off there is a feed C to A at top of MCB
Tested RCD with loads disconnected - functions perfectly.
There is an interlink between circuits A and C - kitchen was wired by clients friend who altered circuits and has obviously mixed up fixed appliance ring with downstairs ring.
Although I am getting continuity between all 4 ends - was hoping to solve problem by making 1 big ring but this is not possible.
Having to go back and try and sort this mess - its a house sale that concludes 4 weeks buyer want EICR seller is client.
Not looking forward to fault finding - all tiled etc may have to consolidate all A and C cables into 1 20A mcb but very reluctant to do this as putting problem onto someone else
So - if all the above is clear can anyone explain why this interconnection between RCD protected circuits prevents and RCD from functioning?
Obviously there is a lesson for me to initially check an RCD that doesn't function with the loads disconnected in future
Many thanks
Many thanks