See im baffled by the ze yes water and gas bond disconected Defo tt even got a note on the cut out dont supply PME ,16mm to 3/8 spike at source then a 16mm 3 core swa via a switch fuse to the DB, i never disconected outgoing neutrals on my rcd test at the unit its self , the testers only 3 months old but im hearing there are issues with the earth pins inside it's a robin MFT going to borrow a mates and see if thats the issue, but i just can't understand one working and the other not. Looking in the board im not 100% its not been adapted from a old 100amp 30/ma split load style and the busbars etc might not be right but it all seemed to be conected fine to me. A longer look maybe required apon my return i think.


An Ra of 0.70 ohms on a 3/8'' twig?? Not even in your wildest dreams!! lol!!!, Even the dammed cable is bigger than the spike it's attached too....
 
An Ra of 0.70 ohms on a 3/8'' twig?? Not even in your wildest dreams!! lol!!!, Even the dammed cable is bigger than the spike it's attached too....

Telling you now ZE of 0.70 droping to around 0.63 on zs I'm curious as to why its so low but thats what im getting, im back next week with a another tester to double check readings
 
just a quick update on this ,Been back today changed the bus bar and fitted 4 seprate rccbos got 3 out 4 curcuits passing the rcd and other relevent tests now just 1 ring to go now that trip for love nor money but ever other test is fine !
 
just a quick update on this ,Been back today changed the bus bar and fitted 4 seprate rccbos got 3 out 4 curcuits passing the rcd and other relevent tests now just 1 ring to go now that trip for love nor money but ever other test is fine !

And the outstanding Ra values on a 3/8th twig??
 
My gut feeling is still a parallel path to a TNCS Connected service of another premises, but as you say huntos33 all other paths disconnected when reading Ze. Nice and chewy
 

Reply to Rcd not tripping when tested ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock