Hi all

I'm stubbed on a new installation which I tested today. It is a M2 split board with a TT earthing system. All test results were fine until I attempted RCD tests. The test button works on both RCD's and the RCD main switch. The main switch is 0.1A and the two RCD's is 0.03A. But they both don't trip when 1x and 5x is attempted on my Fluke. It is a small installation so I checked everything and there is screws etc through anything and the polarity of the RCD is fine.
I haven't changed the RCDs yet as wondering if anyone else has come across this and may know anything else I could check.

Thanks
 
This is the other query as the figure I got was 412 ohms which I believed was to high (200 ohms)but my boss stated it was fine and within 1665 ohms which is acceptable.
 
How many rods and how deep?

I don't know the soil conditions where you are so can't comment on that value without a bit more information. If you've achieved that with multiple long rods then it will probably be stable, or if it's just one little rod then it is unacceptable.

That is a very high Ra but it should not prevent the RCD operating.
Test the RCDs with the outgoing conductors disconnected and see how it goes.
 
I have had a couple of instances with Ra's around 500-600 ohms where the RCD would trip, but not in the permitted times. Both these installs were upgraded to PME and the trip times were then satisfactory. Agree with DS; if it's one four foot rod only then it will likely be unstable and fluctuate markedly.
 
Last edited:

Reply to RCD not tripping in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
771
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock