Discuss RCD problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
R
rlz
Hi
When I do a loop test on an installation protected with an rcd using my robin kmp 4118 (no d lock) the rcd doesnt trip.
Both the tester and rcd have been tested ok by other means - any ideas?
A very frustrated engineer
Agree with Mark on that.
Some manufacturers RCD's or RCBO's wont trip when loop testing.
If they do trip, then the only option normally is to bridge out the RCD temporarily.
RCDs aren't supposed to be bridged out, if the RCD trips the value should be calculated using
Zs=Ze+R1+R2 and then noted on the test sheet
As long as you are confident the RCD AND the Loop tester are functioning correctly then I cant see any problem.
As the above post states Zs can be obtained by calculation ,and in fact in some cases to prevent Live Working... this is the only acceptable method to use.
spark1
Reply to RCD problem in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...