Discuss Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I don't know what the UK regs say about it but it would seem a pointless exercise and unnecessary expense.
 
The way I look at it the TX is an item of equipment so it needs to be fed safely. If the circuit calls for rcd protection then it should be used, before rcd's was also before 11ov on building sites and a lot of accidents happened, thus the implementation of transformers.
If the feed to the transformer is in another building then, if following regs an rcd should be fitted. thats the way I read it anyway.
I've got my blindfold on I've smoked my last cigarette, so fire away.lol
 
do you get 110v from + and - ....or still only 55v.....................would you protect the transformer mcbs with an rcd, if so how would you test the rcd protecting the 110 circuits
 
think it's a hypothetical thread, tony. OP was nearly 2 years ago.
 
As a site transformer should provide isolation between the primary and the centre earthed secondary, I will let you sketch the earth fault current and then present an answer.
 
the l n are seperated but the earth flows back to source....so no.....so if the cable going into the tx is terminated into an rcd this is also primary side and also would not trip if same senario
 
so ive found out that you can test at 55v and the rcd should be on the secondary side and the rcd really should be designed for 110 use, i got there in the end and all the doubters abviously didnt know this....thanks for the pro active comments, all i need to find out now is exactly how you test it
 
you can buy megger rcd testers that let you test 110v cte, and it enables longer lengths of cable curing efli measurements......not sure how effective they are as additional protection......or how you would test the 110v rcd....i suppose using the prongs on the l e and n at end of female plugs........i can understand protecting the armoured with an rcd as the breaker is 50a in my case, but i cant get an rcbo that size.....only saying this as its an electrical forum and if i said this to my mrs she would leave me....---
 

Reply to Rcd Protection For Supply To A Transformer On Construction Site? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
657
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
693
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock