They need additional rcd protection then, why are you trying to avoid it.
i am not trying to avoid i thought because they will be for stereos and computers and not outdoor equipment then they would not need it, also to prevent tripping and knocking half the house out,although a rcbo would sort this
 
personally, I'd fit a dedicated RCBO. then it can be switched off/locked off when his mate wants the kids to go to bed.
 
You can get out of it at present, just by labelling up the socket with the item it is intended for.
When the 18th kicks in, you will have to either provide RCD protection, or cut off the plug and use an SFCU.

Personally, I can see some installations in the future with departures.
 
i am not trying to avoid i thought because they will be for stereos and computers and not outdoor equipment then they would not need it, also to prevent tripping and knocking half the house out,although a rcbo would sort this

The regulations intend RCD protection for all sockets for general use. This is why the exceptions keep getting scaled back in every amendment, because people use them as loopholes to wriggle out of following the intention of the regs.
 
the whole industry has gone too far. next will be writing out a RA to go for a dump.
 
Hi deanmac,

I would like to know why you wouldn't want to rcd protect the circuit?

Also what reason would you put on the risk assessment for not using an rcd?
 
I think they’ve gone a little too far this time.
Totally agree. The specific item clause was very useful for things like roller shutter doors where the units can just be plugged in on install, and other permanently sited items like FLT chargers.
The move to 32A will have quite an affect too, but nothing that can't be overcome without too much hassle.
 
I think in the OPs case he cannot label them for specific use as they could be used for any purpose. If he feels the accumulative loads are likely to result in nuisance tripping he needs to go back to the drawing board or fit individual rcd sockets.
 

Reply to rcd protection on sockets in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock