hi guys if a bank of 20 sockets wired in surface trunking on a radial circuit,these sockets would be used for computers gameboys and music equipment,my question is would they need to be rcd protected ? i know normally they would not,it's just that my mate said if protecting computers they should, i cannot find anything on this
If the said socket outlet circuit is subject to high earth leakage current then the circuit needs to be wired differently than a normal Ring FC or Radial FC as per Regulation 543.7.1.201 information can be found on page 81 OSG and Figures 7.5.3 (1) and 7.5.3 (11) Page 82 OSG
i would be running a separate earth along with dual earth terminals just cannot see anything regarding rcd
to omit RCD protection for these sockets, you would have to do a written risk assessment justifying a reason why. what's to stop someone plugging in a faulty appliance?
these sockets are for my friend and will be solely for computer and stereo equipment and not for outdoor purposes etc
411.3.3 Additional protection requirements for socket-outlets and for the supply of mobile equipment for use outdoors
In AC systems, additional protection by means of an RCD with a rated residual operating current not exceeding 30mA shall be provided for:
(i)socket-outlets with a rated current not exceeding 32A, and
(ii)mobile equipment with a current rating not exceeding 32A for use outdoors.
An exception to (i) is permitted where, other than for an installation in a dwelling, a documented risk assessment determines that RCD protection is not necessary.
Reply to rcd protection on sockets in the UK Electrical Forum area at ElectriciansForums.net
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...