No not new been doing it for years , just a grey area to me of when we should class no RCD to sockets a c2 when it’s a building that’s older and open to public
The age of an installation isn't overly relevant. Code 3 would be a statement of fact that socket outlets do not have additional rcd protection, a recommendation of improvement. Code 2 you are implying a situation warranting urgent attention, if you can justify this with evidence that such a situation is pending then that is acceptable.
 
The age of an installation isn't overly relevant. Code 3 would be a statement of fact that socket outlets do not have additional rcd protection, a recommendation of improvement. Code 2 you are implying a situation warranting urgent attention, if you can justify this with evidence that such a situation is pending then that is acceptable.
So the situation where historically no RCD protection has ever been in place say a 30 year old install and we now have public accessing socket outlets for use and for use of machines plugged into the sockets would that not require RCD protection
 
The fact public have access again is not really relevant they are no different to employed staff they all share the same risk.
 
So the situation where historically no RCD protection has ever been in place say a 30 year old install and we now have public accessing socket outlets for use and for use of machines plugged into the sockets would that not require RCD protection

Historical requirements are irrelevant, you carry out the report to the current version of bs7671.

As such General purpose socket outlets without RCD protection would be coded a minimum C3, however if the lack of RCD protection is considered to be potentially dangerous then a C2 would be appropriate.

If the sockets in question are supplying power to fixed, or not easily movable, equipment such as amusements, are not readily accessible etc etc then I would suggest that maybe they wouldn't need RCD protection at all. And then following suitable assessment of the risks no code may be necessary.
 
Gavin, all you can do is assess whether or not, how likely there is and the severity of a potential danger. The guide to coding hints on this (see post 25#) by indicating what type and use of equipment warrants how you code it. Its your call to determine the potential danger. If you feel certain sockets in the installation warrant a C2 then you code them accordingly otherwise the rest would be a C3.
You can then advise the client to what is the best method of rectification should this be required.
 

Reply to RCD protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
279
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
487
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Evening everyone… I’ve attached pictures for your leisure.. so basically the customer does not have any RCD protection.. 3036 fuseboard is in...
Replies
9
Views
290
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock