slrichardson

When you alter / extend / add circuits on an old rewireable fuse board how would you guys add rcd protection, assuming customer doesn't want new board ( too expensive apparently!!! )
 
i advise on a new board. if not then i will divert the circuit your adding on to though a seperate RCD (40A - depending on circuit) in a small housing just big enough to hold the RCD and change 3036 to a plug in 60898 in the old unit.

there is always the option of RCD fused spurs, or RCD sockets (where applicable and the cable suppying them dont need RCD protection (i.e suface, burried below 50mm)
 
Just for piece of mind I would test the circuit as it stands first before fitting any RCD
 
Last edited by a moderator:

Reply to Rcd protection in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock