Hi Guys, now here's a strange fault.
I have recently installed a new split MK consumer unit.
All circuits have high IR and the RCDs were tested by a Robin tester from all sockets and oven and lighting circuits etc, all good.
When I switch "off" my garage lighting, which is 3 fluro fittings the RCD trips on occasions, I suppose I could disconnect each fitting one at a time to see if the problem stops.
Any ideas would be appreciated.:wink5:
 
Hi, welcome to the forum.

As you say the problem (only?) occurs when switching OFF the garage lighting circuit I am assuming you have checked the otherwise obvious possibility of rainwater or condensation build-up in the garage light fittings/accessories and found this not to be the case.

In that case, it is possible that you have a high standing leakage on the installation due to one or more failing appliance(s). The high standing leakage is not sufficient to trip the RCD by itself, but the addition of the switching transients from the garage lighting circuit is enough to occasionally push the RCD over the tripping point.
Test the leakage current (with a suitable leakage clamp meter) of each of the final circuits (connected to the tripping RCD) one at a time, ideally with all other final circuits isolated. You will probably find that you have one final circuit that has high leakage. Next test each appliance on that final circuit to identify the leaky culprit(s). Fridges, freezers, cookers, immersion heaters, irons and kettles are all frequent suspects.
If you fail to find any abnormally leaky appliances and you are satisfied that the high standing leakage is due to the normal accumulated leakage of the installation. Then you have two options, the best would be to split the final circuits over additional RCDs/RCBOs, however, the cheap short-term fix would be to add a snubber to the garage lighting circuit to tame the switching transients.
 
Last edited by a moderator:
You've hit the nail on the head if it trips when its that circuit, problem with one (or more) of the fittings...garage's have a terrible tendancy to leak, could be water in a fitting...drying out, then leaking again thus causing sporadic tripping. You could have a trapped wire behind one of the flourescents if you've had it off recently, could be a number of things really. After typing that, i've realised you've said when you switch it 'off' ...it could even be a loose connection, and when making/breaking the switch its arching onto the earth terminal.

IR test the garage circuit again.
 

Reply to RCD Spurious Trips in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
768
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock