APE37

-
Reaction score
54
hi guys just looking for some advice.
Trying to test an a type 100a rcd type a with a megger 1552 and testing on ac the tests pass but on switching to dc on x5 tests it is saying it is over 40ms. Am I missing something? Or would it be a raulty rcd?
 
hi guys just looking for some advice.
Trying to test an a type 100a rcd type a with a megger 1552 and testing on ac the tests pass but on switching to dc on x5 tests it is saying it is over 40ms. Am I missing something? Or would it be a raulty rcd?

Edit: I don't think the Megger 1552 can test Type A RCDs? (the DC option is for a different type).

I had to upgrade to a 1700 series to get the option to test Type A.

Is it Hager? If so some of them needed to be tested at 250mA I believe, though i think they may have now come back in line with others to avoid confusion.

View: https://www.youtube.com/watch?v=DlDw3JfVFWI
[automerge]1600515413[/automerge]
Edit: I don't think the Megger 1552 can test Type A RCDs? (the DC option is for a different type).

I had to upgrade to a 1700 series to get the option to test Type A.

Is it Hager? If so some of them needed to be tested at 250mA I believe, though i think they may have now come back in line with others to avoid confusion.

View: https://www.youtube.com/watch?v=DlDw3JfVFWI
I can't actually find confirmation either way which type RCD the 1552 can test - seems to be conflicting advice out there. Type A RCDs need to be tested with pulsating DC - but no idea if that is what the 1552 produces.

At the time, I upgraded to a second hand 1711 because of the 2 wire no trip loop test, and it specifically has the option to switch between A and AC types so that's my main tester now.

Still have the 1552 though as it's a reliable workhorse
 
Last edited:
You don't need to test 100mA RCDs at 5x. This test is only for <=30mA when used for additional protection.
 
Hi guys it is a contactum 100a type A 30ma rcd. Managed to get it tripping. Was testing at the rcd but with mcbs on. When I turned them off I got trip times. Must not be accurate when a load is on the rcd whilst testing. Was told that the megger 1552 was able to test type a.
 

Reply to Rcd testing in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock