Hi all
I was doing a periodic test of a house today and was getting 117m/s for the rcd trip,is this to high?
Whats the maximum allowed?
I know i should know this but have just reached a mental block trying to think of it and I don't have my regs book handy to look at it,Im sure the maxium is the same here in Ireland as it is in Britain..
 
Last edited:

ian.settle1

-
Mentor
Arms
Hi all
I was doing a periodic test of a house today and was getting 117m/s for the rcd trip,is this to high?
Whats the maximum allowed?
I know i should know this but have just reached a mental block trying to think of it and I don't have my regs book handy to look at it,Im sure the maxium is the same here in Ireland as it is in Britain..

On what setting x1 or x5 if the later yes.
 
  • Thread Starter Thread Starter
  • #3
On what setting x1 or x5 if the later yes.

I was doing it at the x1 setting 30mA
 
D

desertbootz

trip current / 2 no trip in 2 secs
trip current < 200ms
5 x trip current < 40ms

You owe me a pint of Guiness
 
  • Thread Starter Thread Starter
  • #6
Thanks lads...
No Guinness though I prefer Irish ale :)
 
Similar question

I have being doing some RCD's tests on a TT system and have been getting some high readings, x 5 117 ms.

The ZS reading was 160 ohms.

Are the RCD's faulty?

Any ideas?
 
E

electro

Hi

RCD sounds fine. I take its a type S which means your trip times are also delayed.

Your ZS reading, what is the mA is your RCD? (160 ohms is well high especially this time of year)
is the installation 16th or 17th edition?
is the land agricultural?

Regards
 
split load board with a 100 ma RCD and two 30 mA RCD's

Was a 16th edition installation, hoseholder wanted the board upgraded before he had a new kitchen fitted.

House is in the country.

Assume the ZS is okay as it's below 200 ohms
 
E

electro

Hi

Yea sorry meant ze, i also just read the post its a house forget the agricultural comment. unless theres a corn crop growing in the living room.

Regards
 
E

electro

Hi

160 ohms may not be stable, as the ground conditions this time of year should give you the best readings..if you tested in the summer you may go over the 200 ohms mark..

Regards
 
G

Guest123

Hey Dave.

So your Ze is actually the RA (rod resistance) which as you say is under the 200 ohm mark, but really should be lower in the current conditions less than 100 I like to aim for.

However if the 5x result is on one of your 30mA RCD's then thats a bit of an issue??
 
Last edited by a moderator:
I think I will change one of the 30 ma RCD's, carry out another test and compare the results with the previous ones, just to prove the RCD is okay.
 
E

electro

Hi

Any think over 40ms on the 30mA will be too high.

Regards
 
Bulk Workwear - Clothing Suppliers for the Whole Forum Network
This official sponsor may provide discounts for members

Reply to RCD trip test maximum reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Top Bottom