I was doing a periodic test of a house today and was getting 117m/s for the rcd trip,is this to high?
Whats the maximum allowed?
I know i should know this but have just reached a mental block trying to think of it and I don't have my regs book handy to look at it,Im sure the maxium is the same here in Ireland as it is in Britain..
 
Last edited:
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

ian.settle1

-
Mentor
Arms
Hi all
I was doing a periodic test of a house today and was getting 117m/s for the rcd trip,is this to high?
Whats the maximum allowed?
I know i should know this but have just reached a mental block trying to think of it and I don't have my regs book handy to look at it,Im sure the maxium is the same here in Ireland as it is in Britain..

On what setting x1 or x5 if the later yes.
 
D

desertbootz

trip current / 2 no trip in 2 secs
trip current < 200ms
5 x trip current < 40ms

You owe me a pint of Guiness
 
Similar question

I have being doing some RCD's tests on a TT system and have been getting some high readings, x 5 117 ms.

The ZS reading was 160 ohms.

Are the RCD's faulty?

Any ideas?
 
E

electro

Hi

RCD sounds fine. I take its a type S which means your trip times are also delayed.

Your ZS reading, what is the mA is your RCD? (160 ohms is well high especially this time of year)
is the installation 16th or 17th edition?
is the land agricultural?

Regards
 
split load board with a 100 ma RCD and two 30 mA RCD's

Was a 16th edition installation, hoseholder wanted the board upgraded before he had a new kitchen fitted.

House is in the country.

Assume the ZS is okay as it's below 200 ohms
 
E

electro

Hi

Yea sorry meant ze, i also just read the post its a house forget the agricultural comment. unless theres a corn crop growing in the living room.

Regards
 
E

electro

Hi

160 ohms may not be stable, as the ground conditions this time of year should give you the best readings..if you tested in the summer you may go over the 200 ohms mark..

Regards
 
G

Guest123

Hey Dave.

So your Ze is actually the RA (rod resistance) which as you say is under the 200 ohm mark, but really should be lower in the current conditions less than 100 I like to aim for.

However if the 5x result is on one of your 30mA RCD's then thats a bit of an issue??
 
Last edited by a moderator:
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members

Reply to RCD trip test maximum reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Top Bottom