Hi

I have just tested a 80A 30mA time delay RCD model MK 5780s.

The times I get are
1/2x - 2000ms at 0 and 180
1x - 0.0ms at 0 and 46.7ms at 180
5x - 10.4ms at 0 and 6.4ms at 180

These don't seem right because I thought time delay RCD should trip at between 130ms and 500ms at 100%

Could someone please confirm this?

Thanks
Mark
 
I see.

The 's' is a reference to the sentry board into which they fit.;)

As for the test results it depends on what flavour of tester you have as >2000ms normally indicates a faliure to trip, which it should be at 0.5x the rated current.

The 1x readings are a bit strange but, the 5x readings seem ok.

Was there a lot of electronic equipment in circuit at the time of test??
 
Ok thanks for that, makes sense now:D

Do I need to unplug everything from the circuit, cos I left the fridge, washing machine, kettle etc plugged in and just unplugged the computers, radio and tv.

Thanks for your reply

Mark
 
If you are getting strange readings then clearing the circuit of all external "noise" would be a step in the right direction.

Dont know which tester you have but the megger stand alone RCD machine is notorious for getting upset with external leakage from appliances and the like.
 
Thanks bud

I'll take everything off the circuit and see if it improves, I am using a Fluke 1652:D

Thanks bud

I just unplugged the lot and got much better readings.

1x at 35.8ms and 62.5ms
5x at 11.0ms and 6.4ms

Cheers:D
 
Last edited:

Reply to RCD trip times in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
733
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
I've started to move over to AMD 2 forms for my CU installs, if only because the schedule is so much easier to tick and I can stop sticking labels...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock