Before I go any further can you tell me where the RCBO is in the DB is it next to the Main switch? i'm wondering if it has been positioned on the busbar which is controlled by the rcd the easiest way to determine this is the switch off the RCD and see if you still have power to the heating system. a picture speaks a thousand words? please let me know of your findings.
 
This is a curious point.... It's so fundamental it would be easy to overlook. If the RCBO has been put on the RCD protected side by mistake, then a modest amount of leakage from the heating system would still tend to trip the RCD before the RCBO due to the additional leakage from the rest of the installation.

It seems unlikely that only the RCBO's neutral would be in the wrong busbar as mentioned earlier, because any heating system load should then cause an immediate trip.
 
This is a curious point.... It's so fundamental it would be easy to overlook. If the RCBO has been put on the RCD protected side by mistake, then a modest amount of leakage from the heating system would still tend to trip the RCD before the RCBO due to the additional leakage from the rest of the installation.

It seems unlikely that only the RCBO's neutral would be in the wrong busbar as mentioned earlier, because any heating system load should then cause an immediate trip.
My thoughts were the live on the wrong bus bar or neutral in the wrong bar could well be causing this issue I have seen this before the biggest trouble is that the load is very minimal on the heating system.
 
Many apologies for not responding for several days but I've been diverted onto other domestic issues! The consumer unit is not very obvious to follow so I've drawn a schematic to show how it all fits together. It has been modified because originally it was thought that the central heating was causing the tripping problem, so it was put on an RCBO. That didn't cure the problem, so Sockets 2 was moved onto a separate RCD. By the way, MCBs on the Sockets 1 RCD include the fridge, cooker and freezer. The only other item on the Sockets 2 side is the Photovoltaic panels.

I am convinced the Sockets 2 RCD tripping is indirectly connected to the central heating. It trips every day now, between half an hour and an hour after the c/h comes on.

I'd be really grateful for any further suggestions I could discuss with the electrician when he comes later this week.
 

Attachments

  • Schematic.jpg
    57.8 KB · Views: 13

Reply to RCD tripped by central heating which is on a separate circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock