Kyanther

DIY
Reaction score
2
I have a 40amp trip on my main consumer unit feeding my workshop where I have another consumer unit with 1x6 amp 2x16 amp and 1x32amp trips. I've replaced my old 3hp tablesaw that was run from a 13 amp plug on the 32amp ring with a new 3hp one that is plugged into a 16amp socket through a 20amp isolation switch and into its own 16amp trip.
Is there any reason other than a fault with machine why the new machine is tripping the house Rcd?
Hope this makes sense
Thanks
 
Tripping the RCD is a little worrying, as a new saw should not have any significant earth leakage.

However, you might have a N-E fault that is not normally apparent but now the start-up current of the table saw is enough to cause a current imbalance large enough to trip the house RCD.

So I would advise that you get a professional sparky in to check out your saw and the house wiring to see what the real reason is behind the nuisance tripping.
 
Was the 16amp plug already on the saw and was the 16amp socket already in the workshop and has previously been used with no issues?

As my guess would be the 16amp plug or socket is wired up wrong, N & E reversed in one of them, if either have recently been fitted.
 
Thank you for the replies. N + E checked and not reversed. Yes plug was on machine and welder works fine on socket.
[automerge]1593985289[/automerge]
I've temporarily fitted a 13amp plug and put it into ring main only as a test and it still trips the house rcd.
 
Can you show a pic of the 40A device which is tripping because a single phase 3hp motor will take between 45 and 50A on start up.
 
Thank you for the replies. N + E checked and not reversed.
You need to check for a N to E short somewhere within the wiring as well.

Normally N & E are essentially at the same 0V potential. But if you get a lot of current going through N (for example, on motor start up) then there will be a voltage drop and if there is an insulation fault to E then it will divert some current, and so trip a RCD.
[automerge]1594021671[/automerge]
Of course, it is also important to check the saw in case it has some fault leading to current going to E.
 
Last edited:
Agree with above, either the saw is faulty or there is a neutral-earth fault one one of the circuits protected by the RCD that trips, that is being revealed by the high starting current of the saw. It is not necessarily the circuit that the saw is plugged into that is faulty. Either way, insulation test results are needed to progress the diagnosis any further.
 
Thank you all. I've got an engineer from Axminster tools coming to change the motor at the end of the week. So we'll see if that fixes the problem if not I'll get those earth tests done!
 

Reply to Rcd tripping from new 3hp tablesaw in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Replies
18
Views
1K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
781
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
931
I have a fairly recently installed consumer unit with an RCD, between it and the garden there is another, much older (25yrs?) RCB (big Wylex...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock