Discuss RCD tripping. Give me a clue! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Piratepete

Hi Guys
A Happy 2014 to you all.
I've recently had two calls to trace the cause of intermittent tripping in domestic installations, and failed miserably!

The latest - 4 way box feeding garage, utility room, garden shed. Customer reckons it sometimes trips when they switch the light on, but can trip without any human intervention.
RCD is fine. Also did a ramp test - 22mA Ok.
IR - 1.47 Meg for L+N of all circuits to Earth with everything plugged in. So it's a bit low but not anywhere near low enough to trip the RCD.
Two fridge freezers - I've been told that these are prone to high earth currents - measured under 1 mA.
Washing machine and tumble drier are usually turned off at socket. Doesn't trip while they're running.

Any bright ideas to track this fault, please?

Cheers!
Pete
 
once you have eliminated the impossible, whatever remains, however improbable, must be the truth.
 
1.4 Megs is a bit on the lowside and might not be a stable reading. It would probably at least warrant localising then make a decision if it's worth remedial work.

If you can't see a sufficiently low IR with a Mega tester then use an earth leakage clamp meter around the L&N simultaneously and monitor over time and under different load profiles.
 
Could be a collective earth fault. Add up all the leakage from the appliances with a clamp meter and see just how many milliamps are leaking. You may have to split the circuits over different RCBOs/ RCDs
 
To properly investigate low IR you need to disconnect EVERTHING and IR all 3 cores.
I would've thought that a general IR was adequate. Seperating the circuits will only result in increased IR readings - worst case will be one circuit at 1.47Mohm -This is not low enough to trip an RCD.
 
Could be a collective earth fault. Add up all the leakage from the appliances with a clamp meter and see just how many milliamps are leaking. You may have to split the circuits over different RCBOs/ RCDs

Good idea along with Marvo's suggestion,above. I don't currently possess a clampmeter that's sesitive enough. Still saving up for that torque driver that I need to do up CU screws correctly:hammer:. Could use my inline meter to check overall earth leakage. All depends whether my customer wants to spend the money!
 
I don't know what you're getting at here. How will disconnecting everything affect the ramp test? The only thing switched on was a light.

You are testing the RCD only.
Testing with circuits connected could result in false readings due to leakage on the circuits.
At the very least, turn all the MCBs fed by the RCD off.

It's GN3 somewhere...I think! :)
 
Why do an IR with everything plugged in?

Because that is the situation when the RCD trips, which could be caused by an appliance. If I'd found an exceptionally low IR, I'd then unplug everything and retest, to see if an appliance was at fault. The fallacy with this is that some faults don't show up unless the appliance is actually running - washing m/c pump motors comes to mind.
 
Good idea along with Marvo's suggestion,above. I don't currently possess a clampmeter that's sesitive enough. Still saving up for that torque driver that I need to do up CU screws correctly:hammer:. Could use my inline meter to check overall earth leakage. All depends whether my customer wants to spend the money!

Forget the torque driver, an earth leakage clamp meter would be more important.

You can't use an inline ammeter to check leakage current because it will only tell you what's going down the CPC, not what's being lost down parallel paths. The RCD doesn't monitor the CPC current so the test would be meaningless.
 
You are testing the RCD only.
Testing with circuits connected could result in false readings due to leakage on the circuits.
At the very least, turn all the MCBs fed by the RCD off.

It's GN3 somewhere...I think! :)

Ok. Point taken, but if there is existing leakage, say 5 mA, and the ramp test shows 22 mA, then the tripping current for the RCD is 27 mA, I think.
 
Yep, but if there happens to be 9mA leakage and your ramp test shows a pass at 22mA then you will leave a non-compliant RCDin service thinking it's okay.
 
Forget the torque driver, an earth leakage clamp meter would be more important.

You can't use an inline ammeter to check leakage current because it will only tell you what's going down the CPC, not what's being lost down parallel paths. The RCD doesn't monitor the CPC current so the test would be meaningless.

Good point! Can you recommend a suitable meter.

I accept that the RCD is looking at an imbalance between L and N. Isn't that difference also reflected in the main cpc?
 
I think many of the UK guys seem to use a Dialog earth leakage clamp meter which I believe is very reasonably priced. I'm sure someone will chip in with the exact model number for you.

Not all fault currents flow down the CPC, for example if an appliance has an IR fault and happens to be in contact with the kitchen sink then the fault current or a good portion of it will flow to earth through the water pipework and/or the earth bonding.
 
A common one is fridge and freezer compressors,these can test out OK but when they have run for a while and heat up they reveal a fault,that can be a real pain to find.
 
Do you not think 1.47 Mohms is a low reading?

Doesn't GN3 state 1Mohm is acceptable reading but anything less than 2Mohms requires further investigation.

Not sure why your testing with everything plugged in? Not sure what this achieves?

The chances are 1.47 Mohms is probably due to it reading through an appliance.

Remove the appliances, lamps, etc. and retest IR on each circuit, see if the readings improve (I guess they will).

If they do try PAT testing each appliance, if one looks dodge exclude it from circuit for few days see if that helps.

Trial & error only way forward if it's an appliance at fault
 

Reply to RCD tripping. Give me a clue! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Feel like I’m posting on here every week for advice :) is a reading of 0.18 megaohms between neutral and earth enough to trip and RCD. Sent to an...
Replies
5
Views
2K
Morning, Customer has a intermittent trip which I am trying to locate. 4 circuits on rcd. Two rings , cooker and hob and one I cannot find...
Replies
4
Views
3K
So to start off with i’ll tell you i’m a young electrician, 23, I am qualified but obviously will always be learning. Was carrying out an eicr...
Replies
4
Views
2K
Hi guys, first time poster, be easy! I'm caring for a friend and last night while sleeping on the sofa-bed an emergency system that had lost...
Replies
44
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock