First time poster go easy on me.

Got a call out to a job today, got told the RCD was tripping. Even when no appliances plugged in. And so it was intermittently about every 20 mins. Only two ring circuits on the RCD, on one of the rings im getting continuity across line and netural on both legs. Its not taking the MCB out, no fault across the earth.

Tested the RCD for nuisance tripping all passed fine.

Cant get my head around why with a permanent short the MCB wont trip? Going back tomorrow morning for further investigation and feeling as if i should suggest re wire of sockets due to reasonably low IR readings anyway.

Any thoughts would be appreciated.
Cheers
 

SparkyChick

Mod
Mentor
Arms
Esteemed
Welcome to the forums.

When you say continuity... what kind of readings are you getting Line to Neutral? I'm suspecting they are not shorts but some appliance.

Why do I say that? Because a line/neutral fault won't trip the RCD because even under a direct short, the current flowing in line will be the same as that flowing in neutral and the RCD will quite happily sit there.

What IR readings were you getting?
 
  • Thread Starter Thread Starter
  • #3
Cant remember the exact values on continuity, but it was a high level of resistance.

There are some kitchen appliances left to be checked, but those are on fused spurs so i suppose a fault could still come back up the netural if only single pole switch.

IR getting >0012 and i know its technically acceptable but its pretty low and makes me feel a bit uneasy.
 

SparkyChick

Mod
Mentor
Arms
Esteemed
If you're getting continuity but a high resistance, then it's more like to be something plugged in/connected.

The IR reading is that L and N to earth, or L to earth, N to earth, L to N? And is that 1.2Mohms?
 

Matthewd29

-
Arms
Esteemed
Is there any chance there's an exterior light wired out the back of one of the sockets that might have damp in it? I've seen this happen many times
 

123

-
Arms
Esteemed
First time poster go easy on me.

Got a call out to a job today, got told the RCD was tripping. Even when no appliances plugged in. And so it was intermittently about every 20 mins. Only two ring circuits on the RCD, on one of the rings im getting continuity across line and netural on both legs. Its not taking the MCB out, no fault across the earth.

Tested the RCD for nuisance tripping all passed fine.

Cant get my head around why with a permanent short the MCB wont trip? Going back tomorrow morning for further investigation and feeling as if i should suggest re wire of sockets due to reasonably low IR readings anyway.

Any thoughts would be appreciated.
Cheers
Find the fault, fix the fault. Don't just go rewiring a circuit because there is a fault on it.
As the fault is still not found it could be literally anything, faulty appliance, central heating pump, damp, damaged cable and many more. Find where the fault is first, then come up with the solution.
 

Pete999

-
Arms
Esteemed
Cant remember the exact values on continuity, but it was a high level of resistance.

There are some kitchen appliances left to be checked, but those are on fused spurs so i suppose a fault could still come back up the netural if only single pole switch.

IR getting >0012 and i know its technically acceptable but its pretty low and makes me feel a bit uneasy.
IR > 0012??
 