Ok help before a pull out the rest of my hair got an rcd that trips when ring main breaker turned on got continuity but still trips when only live connected ant ideas
 
Aico 3000
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
D

Daveh36

-
  • Thread Starter Thread Starter
  • #3
ok so just changed a board connected everything back up and was tripping on lights or so I thought so disconnected them. no all I have connected in board is two lives for ring main and rcd trips when ever I turn the breaker on
 
John Preston

John Preston

-
You say you only have 2 lives connected. No earth or neutrals connected?
 
D

Daveh36

-
  • Thread Starter Thread Starter
  • #5
yep disconnected everything trying to check whether a neutral was crossed or something literally pulling my hair out now
 
D

Daveh36

-
  • Thread Starter Thread Starter
  • #11
ok so got continuity not shorts insulation resistance low but not too low at 16meg and again all I have connected or two lives of the ring no neutrals for any circuit no earths for any circuit. RCD stays on until I turn the breaker on. Never come across a fault like it
 
Strima

Strima

-
Esteemed
Arms
IR test done with all earths connected? Sounds like you have a path to earth somewhere.

If there's a boiler or other fixed appliance on the circuit check for reversed polarity.
 