I always been told that an 30m/A RCD should trip within 200m/s (x1) and 40m/s (x5). But something iv never taken much notice of before is on test sheet the maximum disconnection time of a circuit less than 32A is 0.4. So....which is it? within 0.4 or within 200m/s????
 
0.4s = 400ms for TN disconnection times<= In 32A, and 5s for >32A In or distribution circuits.

for TT 0.2s and 1s respectively

An RCD/RBO is faster in both cases, 40ms (@5XIdn) = 0.04s
 
Last edited:
So the max disconnection time for a circuit <32A is 400m/s. Yet the RCD has to trip <300m/s? Are you saying an MCB's max d/connection time is <400m/s? If so there is no way to test the tripping time of an MCB as far as i know? :S
 
Circuits supplied by a TN system, as it stands at present, should be designed to disconnect in 0.4sec. It is a comparatively modern idea to use RCDs/RCBOs on all circuits (Its very European you know !)

See 411.3.2

RCDs are used to provide additional protection, but can also be used as fault protection where the normal method is for some reason insufficient to give a disconnection time less than Table 41.1.
 
If the RCD is for 30mA or less, and used for additional protection, then this is tested @ 5X Idn and should trip in less than 40ms, (I have missed out the 1/2 Idn,1X Idn and 0 and 180 degrees etc. for clarity), all other RCD's (100mA etc.. used for dist. circuits) are only tested at 1/2 and Idn, does this help ?

30mA or less RCD's are for additional protection of final circuits.

Actually one more question. How can you test that a circuit disconnects in <400ms (0.4) if it has no RCD on it?​

By calculation (max Zs etc.) and the tripping curves in the BGB, you have to just take this at face value, as we lowly sparks do not have the equipment to test this.
 
Last edited:
Lets say iv got a circuit. Its TNCS and its on a 10A MCB and has a 63A, 30m/A RCD covering it. If i do an RCD test its should trip out in <300m/s yes?

It will depend what the current flow is at the time of disconnection.

To meet the requirements of BS 7671 it must trip out at <=300ms at its IAN, and 40ms at 5 times its IAN

An earth fault current of minimal impedance covered by a 10A MCB will disconnect as fast as an RCD, probably quicker. Some manufacturers have data sheets showing a likely disconnection of 0.01s.
 
quick question as well re RCDs, testing a village hall with 30ma up front of everthing rcd trips on 1/2 test With message TRP on the tester fine at x1 28 ms, same as 1/2 on x5 trips with TRP message, checked the booklet with the tester says that message is leekage on the curcuit, but its the same for all 16 curcuits, TT system 194 oms RA sound like a faultly trip ? All insulation test are >500 .
 
quick question as well re RCDs, testing a village hall with 30ma up front of everthing rcd trips on 1/2 test With message TRP on the tester fine at x1 28 ms, same as 1/2 on x5 trips with TRP message, checked the booklet with the tester says that message is leekage on the curcuit, but its the same for all 16 curcuits, TT system 194 oms RA sound like a faultly trip ? All insulation test are >500 .


You should be testing at the load terminals of the RCD with the circuit/load cables disconnected. You won't see any natural leakage then... What do you expect with 16 circuits being monitored??
 
I would do a ramp test and see what value it is actually tripping at with everything disconnected, it could be that on a single up front RCD that you have too much (normal) leakage, which is pushing it over the edge at 1/2Idn, and of course as you know, it should not trip at 1/2Idn.
 
I would do a ramp test and see what value it is actually tripping at with everything disconnected, it could be that on a single up front RCD that you have too much (normal) leakage, which is pushing it over the edge at 1/2Idn, and of course as you know, it should not trip at 1/2Idn.

The ramp test came in at 18ms with all curcuits/loads which can effect readings off.
 

Reply to RCD tripping times, 0.4 or <200 etc..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Im suppling distribution circuits and want to use the largest possible RCD available to avoid nuisiance tripping (its for outdoor street furniture...
Replies
2
Views
871
Hello all I have recently installed a sub main in 4mm 3-core SWA, approx length 45 metres, to feed a small garden office. Final circuits in the...
Replies
7
Views
2K
So to start off with i’ll tell you i’m a young electrician, 23, I am qualified but obviously will always be learning. Was carrying out an eicr...
Replies
4
Views
2K
Hi Have a nightly problem - will be changing a consumer unit however have a problem customer has an older mem m6 32amp rcd/mcb on downstairs ring...
Replies
10
Views
4K
Hi I'm removing an extractor fan from our WC, as it's just a toilet and sink and we never use hot water in there anyway... The extractor is on...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock