Discuss RCD Tripping under No Load!! in the UK Electrical Forum area at ElectriciansForums.net
N
nate1880
Hi Folks,
I'm new to this forum. Got a bit of a head scratcher for you all.
I have recently installed a new dual rcd consumer unit in a retirement home apartment It is about the 20th apartment we have done with no previous problems whatsoever.
On energizing the consumer unit I switched on the main switch, then both rcd's.
One by one I switched on the breakers and everything was fine, went in to each room operating the light, the lights all worked correctly but when I got to the kitchen light and operated the switch the rcd on the opposite side to the one protecting the lighting circuit tripped??
I flicked it back on, tried operating the test button for both RCD's, RCD 1 the one not protecting the lighting circuit would not operate, RCD 2 the one protecting the lighting circuit operated fine.
So I thought, ok dodgy RCD, so replaced the RCD, same problem occurring.
I have thought of everything , there is no damaged cables, no 'borrowed neutrals', the consumer units internal links are all wired correctly, everything looks correct but something is a miss & I cannot think for the life of me what?
Now the RCD will not even hold at all, flick the main switch on, flick on RCD1 & it's trips instantly. With no load.
Thanks in advance for any advice offered.
As DW mentioned, might be best to get the wires back out of the board and test each cct. Don't think I have ever changed an RCD under such circumstances as there are plenty of ways to find out whether it really is the RCD or a fault on the wiring or appliance
Crossed/borrowed neutrals maybe, the RCD tripping might be marginally faster than the other one. Could also be N-E insulation value but you'd have picked this up on the dead tests before powering up surely. The chances of it being a fault with the actual RCD is extremely slim and running an RCD test would be better proof of correct function than just replacing.
Hi Folks,
As it's still tripping I'd suggest not....:wink_smile:
Reply to RCD Tripping under No Load!! in the UK Electrical Forum area at ElectriciansForums.net
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...