Email from customer:

Our Solar PV installation is protected by a 30mA RCD in it's own CU which regularly trips during the morning inverter startup at this time of year (when the roof is persistently very wet). We have a transformerless grid-connected Power One Aurora inverter, and I understand the 30mA RCD is just a little too sensitive.

Been a long time since I've done PV! I've got no other info, so don't know where the invgfertor is sited.

Just checked a Power One manual and no mention of RCD protection needed, so if no cables are concealed he doesn't really need an RCD, if its not TT?

Any recommendations for tansformerless invertors needing RCD protection?
 
If it doesn't need RCD protection to protect the cable - ie unless it's buried less than 50mm in a wall, then it doesn't need an RCD / could be put on a 100mA.
 

Reply to RCD tripping in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock