So the garage is without an electrical supply, so I decided to install one.

I laid about 20M of 2 core 2.5mm2 armoured cable and terminated it in the garage with a consumer unit.

Added a metal clad double socket again supplied by 2.5mm2 - all mounted on a large sturdy wood board and encased in trunking.

Ran separate trunking with 1.5mm2 to a strip LED light in the centre on the ceiling with a pull switch.

I tested the installation initially with meter and then live with an extension in the house run to a 13amp socket and it all worked perfectly.

I finally wired it into the main fuse box but now it immediately trips the RCD.

OK the obvious conclusion is that somewhere I have a leakage of current to earth BUT the aforementioned socket is wired through the main distribution board through the RCD. I have checked that the MCB supplying the socket is protected by the RCD - it is.

So the RCD does trip when it's supplying current through the socket outlet bit does trip when it supplies current through a new MCB.

Curious.

Any technical solutions please.
 
As above, it sounds likely that you have incorrectly terminated the N in the house DB. Bear in mind this installation requires notification to BC, if you fail to do so and have not installed and tested it in accordance with Bs7671 you are breaking the law.
 
well done for owning up. bet there's a lot more members wot have done that at some time, but won't admit to it. i know i did it once and had a shower replaced before i spotted it. to be fair though, there weren't enough N terminals on the correct bar.
 

Reply to RCD Tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
566
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
315
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock