I have been doing a periodic test on a property for a guy i do alot of work for, there was loads of things wrong no gas or water bond there was a sub main in the main house that was over 3 meters away from the mains with just tails coming out a henley block feeding it, also its a tt system so its just using a main rcd that wasnt tripping in under 0.4 seconds so I have changed it today put everything back on all fine nothing tripped did an rcd test all good also did a quick loop test everything fine, I have since come home then the guy has phoned me up he has no power the rcd has tripped I just thought nusiance tripping, but now the rcd is randomly tripping and wont trip under rcd test and now i cant loop test it just trips the rcd out, I have manged to get everything back on and holding in, I have just got home and cant think why it would be doing it any ideas?

thanks

Billy
 
May seem like a long shot but it could be the rcd. I have had two brand new ones(from different manufactures) recently test fine initially but a day later trip and then the test button would not work and they had to be returned. I had every socket cover off as I could not believe it could be the RCD. I now will only fit RCBOS to new boards as at least that way you can identify the circuit easily in the event of a fault. Good luck,
 
I have been doing a periodic test on a property for a guy i do alot of work for, there was loads of things wrong no gas or water bond there was a sub main in the main house that was over 3 meters away from the mains with just tails coming out a henley block feeding it, also its a tt system so its just using a main rcd that wasnt tripping in under 0.4 seconds so I have changed it today put everything back on all fine nothing tripped did an rcd test all good also did a quick loop test everything fine, I have since come home then the guy has phoned me up he has no power the rcd has tripped I just thought nusiance tripping, but now the rcd is randomly tripping and wont trip under rcd test and now i cant loop test it just trips the rcd out, I have manged to get everything back on and holding in, I have just got home and cant think why it would be doing it any ideas?

thanks

Billy

You don't mention anything regarding insulation resistance readings....

Was the existing RCD time delayed?
 
Last edited:
yeah rcbos are definatly much better at least you dont lose evrything in one hit, I havent actually changed the board in this case its a newish board old style mk board so just fitted a new rcd as the old rcd wasnt tripping in .4 secs, the only conclusion I can come to is its a faulty rcd, cant really see it being anything else. will pick one up first thing and change it fingers crossed thats what it is.
 
You don't mention anything regarding insulation resistance readings....

Was the existing RCD time delayed?

Hi yeah sorry didnt mention that insulation resistance was all clear on every circuit, so it cant be that, yeah the existing rcd time was delayed hence the change of a new rcd, so changed the rcd tested it worked fine also did a quick loop test and that was fine, packed up went home and then got a call to say he had no power, now when I test the rcd I get nothing it doesnt even test and when I do loop test it knocks the rcd out
 
Hi yeah sorry didnt mention that insulation resistance was all clear on every circuit, so it cant be that, yeah the existing rcd time was delayed hence the change of a new rcd, so changed the rcd tested it worked fine also did a quick loop test and that was fine, packed up went home and then got a call to say he had no power, now when I test the rcd I get nothing it doesnt even test and when I do loop test it knocks the rcd out

When you say you do loop tests, are they 'no trip' loop tests or full current?
 
Last edited:
If it tripped on 'no trip' then it would suggest a good few milliamps are already being seen and the 5 or so milliamps of test current are tipping it over.

Try a ramp test and see where the RCD is tripping.

Were/are RCBO's in use for the sub-circuits?
 
yeah it did trip on no trip. thats a good idea I will try the ramp test going back there first thing, there are no rcbos there is a sub main that has rcd protection then just mcbs.
 

Reply to RCD Tripping in the Australia area at ElectriciansForums.net

Similar Threads

Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
735
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
758
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock