Discuss Rcd tripping ???? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Here is the step up16 x 247 w mountef on metal roof Sb 4000 tl On a submain with rcd protecting inverter , lights and powet Few weeks ago rcd triped . Clieny turned off inverter call meI got there and reset the inverter Every ok waited around nothingI noticed a light switch flashing when turned on So i had a look loose cable sorted it.Anyway i have had same call again TodayClient seems to think whem it rains it trips ??? Any advice would be goooood
i wouild be looking for water ingress. might be an idea to ramp test the RCD.
could this be anything to do with the d.c lets say if water enters panel connection boxes or mc4 connection would it trip rcd ??????? if connected in inverter ?????
ie can D.C side TRIP RCD ????
Im Not an expert on Inverters but as the DC side is Class 2 and therefore not normally earthed (Is It earthed?) I would be surprised if it could trip an RCD on the AC side due to water. Don't Sunny Boy recommend using a Type B Breaker?
Yeah , just odd the client said he sparys the array with his hose and the RCD trips nut there are also Lights and power on the RCD SIDE , so my plan is to disconnet the d.c from inverter , give it a blast of water see if it trips ,
I did earth the array frame due to it being a metal roof & structure ??????? what you think could this be doing somthing ?
Is the metal roof also bonded?
I don't thnk this is a PV array problem, I think there is earth leakage elsewhere from another circuit. I agree with Smiffy - try disconnecting the bond from the array and see what happens.
Is this one of these inverters that is transformerless but don't require a B type RCD ?
If it is then it maybe high protective conductor currents in play, as the inverter would leak them and if it's on an existing RCD where there is other equipment on it such as a washing machine. computer then it maybe enough to trip the RCD.
Do a ramp test on the RCD and see what it trips out at. Then check the CPC's which that RCD protects with equipment that is likely to have high protective conductors switch on and see what you get.
Did he use a power washer ? obviously this would'nt account for it tripping during rainfall.
Reply to Rcd tripping ???? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
No lighting has been changed in the house for at least 12 months. Last night a small pop similar to that of a small firework in the distance came...
Hi Hoping to get some insight from people, as I have had two electricians check the fault, to no avail. The most obvious fault is the RCD is...
Hi all. Please be patient as I don't know much about electrics! We had a powercut in the area Tuesday 9th November afternoon - blown fuses in the...
6K